Breakers
We have a 2019 Montana legacy 3730fl. Whenever I use my electric fry pan in kitchen I blow the breaker if the tv and fireplace are on, is this normal? I can’t use any electrical appliance if the tv and fireplace are on.
Thanks for any input.
|
|
|
01-27-2019, 11:10 AM
|
#2
|
Site Team
Join Date: Jun 2011
Location: Wilsey
Posts: 18,799
M.O.C. #11455
|
It sounds like you aren't wired properly. The fireplace should be on a seperate breaker, not part of the kitchen or island system. Also, unless you're using the fry pan in a strange spot, it should be on a GFI circuit.
__________________
Dick, Joyce, Diego, Picatso and Gustav
2017 3720 RL, and 2013 HC 343RL
Pullrite Hitch, IS, Disk Brakes, 3rd AC, Winegard Traveler, Bathroom door mod, Dometic 320, couch for desk swap, replaced chairs, sun screens, added awnings, etc.
|
|
|
01-27-2019, 11:21 AM
|
#3
|
Established Member
Join Date: Sep 2018
Location: Port Rowan
Posts: 18
M.O.C. #22747
|
Quote:
Originally Posted by DQDick
It sounds like you aren't wired properly. The fireplace should be on a seperate breaker, not part of the kitchen or island system. Also, unless you're using the fry pan in a strange spot, it should be on a GFI circuit.
|
Fry pan is on gfi circuit on island. Tv, fireplace and fry pan all go at once. If I plug vacuum in gfi tv and vacuum blow breaker too. Husband was going to put in a 20 amp breaker but dealer said you couldn’t wasn’t safe.
|
|
|
01-27-2019, 01:21 PM
|
#4
|
Montana Master
Join Date: Jan 2018
Location: Thornville
Posts: 546
M.O.C. #21110
|
You have to many things on that one breaker. Amp draw is too high for that breaker. I would put the fireplace onto a different breaker, that should solve the issue.
__________________
Darwin & Carla
2018.5 3701LK Montana
2022 3500HD Denali Duramax SRW
|
|
|
01-27-2019, 02:42 PM
|
#5
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,361
M.O.C. #6433
|
No surprise the fireplace and electric fry pan would trip a 15 amp breaker. But wire is probably not sized for a 20 amp breaker. Best solution would be to add a new breaker and reroute the wire of one of those to that new breaker. But may not be an easy task depending on how your current wiring is routed.
Less desirable option is to always turn off fireplace to use fry pan.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
01-27-2019, 06:10 PM
|
#6
|
Montana Fan
Join Date: Jun 2018
Location: Holladay
Posts: 209
M.O.C. #22087
|
Take it back and get it fixed. Just like DQ said, it sounds like it is wired wrong. TV and fireplace should not be on the same GFI as the kitchen and bathroom.
__________________
2019 HC 381TH
2021 Ram 3500 6.7 HO
|
|
|
02-12-2019, 06:07 PM
|
#7
|
Seasoned Camper
Join Date: Nov 2011
Location: Ringgold
Posts: 55
M.O.C. #11997
|
Fireplace should be on it's own 20 amp circuit.
__________________
2018 Silverado 3500 DRW
2011 Montana Mountaineer 285RLD
|
|
|
02-12-2019, 06:38 PM
|
#8
|
Montana Master
Join Date: Aug 2018
Location: Minden - NV
Posts: 507
M.O.C. #22360
|
There is no separate breaker for the fireplace in my 2019. There's just no room is that small panel they put in trailers for extra circuits like installed in a typical home.
You could install a tandem breaker and pull a separate wire to the fireplace so it would have its own 15A or 20A circuit.
__________________
2013 F350 Lariat Ultimate CC LB
2019 3790RD
|
|
|
02-13-2019, 08:15 AM
|
#9
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,361
M.O.C. #6433
|
Quote:
Originally Posted by jetskier
.......
You could install a tandem breaker and pull a separate wire to the fireplace so it would have its own 15A or 20A circuit.
|
My breaker panel has some spare spaces, and yet they used a couple of tandem breakers any way.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
02-13-2019, 01:38 PM
|
#10
|
Montana Master
Join Date: Oct 2012
Location: Box Elder
Posts: 4,774
M.O.C. #12947
|
Even if you had a 20 amp circuit that went to both the fireplace and your kitchen GFI, you still would not be able to use both the fireplace and electric fry pan together. Your fry pan is probably drawing 1500 watts, and that is the same load as the fireplace. Together, 3,000 watts is 25 amps of load, and that is why they should have had the fireplace on it's own circuit of at least 15 amps. Maybe you can set up the fry pan on the table and plug it into a circuit not on the kitchen breaker, or just use the furnace when frying.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
|
|
|
02-13-2019, 04:45 PM
|
#11
|
Montana Fan
Join Date: May 2015
Location: Livermore
Posts: 492
M.O.C. #17391
|
Do not replace the breaker with a higher amp breaker. The wires aren't made for that much of a amp draw and will get hot and fire will result. Not sure how you can rewire the fireplace on a separate circuit with the wires inside the walls. You should ask your dealer to fix this. Fire place should have it's own circuit.
|
|
|
|