A member’s Dometic RM2852 abruptly stopped cooling with no ammonia smell, normal front lights, and no check light. After using the service manual and meter tests, they found the flame stayed lit, the electric element drew within spec, and the thermistor tested within range, but after two hours with forced heating the freezer was still about 81 degrees, leading the manual’s flow chart to point toward a plugged, non-serviceable cooling unit.
Members discussed that control boards and sensors...
More...
A member’s Dometic RM2852 abruptly stopped cooling with no ammonia smell, normal front lights, and no check light. After using the service manual and meter tests, they found the flame stayed lit, the electric element drew within spec, and the thermistor tested within range, but after two hours with forced heating the freezer was still about 81 degrees, leading the manual’s flow chart to point toward a plugged, non-serviceable cooling unit.
Members discussed that control boards and sensors are common failure points, but the reported forced-operation test made a cooling unit problem more likely. Options raised included replacing the cooling unit, using an Amish-built replacement cooling unit, converting to a 12-volt compressor refrigerator, or installing a residential 120 VAC refrigerator; the original poster planned one more quick check for a possible chimney obstruction before deciding, and noted a 10.1 cu ft residential unit would fit and be supportable by their existing lithium, solar, inverter, and DC-to-DC charging setup.