2012 Montana Furnace Not Starting Consistently at CCC2 Set Temperature

Suzphil20

New Member
Joined
Oct 12, 2023
Posts
3
Location
Waldoboro
We have a 2012 montana that recently developed problem with what we believe is the thermostat. Dometic ccc2 that controls A/C, propane furnace, and fan. A/C, fan work perfectly, by the thermostat. The furnace works, however it will not come on by set temperature consistently on the thermostat. We have done many resets, turned breakers off for the recommended times, unplugged it, let it sit many times.
There are no codes showing on the display and haven't been since problem started
 
The Zone 1 roof AC unit control box is where the Furnace gets its signal to turn on from.... if the Tstat sends the signal to the control box then the two blue signal wires at the control box merely complete the connection at the furnace control board to run the blower and go thru start up sequence...

The CCC2 then looks at the Furnace set point temp versus the remote temp sensor for zone 1... if the temp is higher from Zone 1 remote sensor then Tstat set point furnace wont run...

How that remote temp sensor is mounted on the wall affects what actual ambient air temp the sensor sees.... if the sensor is sitting slightly inside the wall it cant sense accurate actual room air temp...

Resets and turning breakers off wont fix the issue you are seeing... looking at the location of that remote temp sensor for Zone 1 verus its placement on the wall will make a difference...

Example... my Zone 1 remote temp sensor is located in the kitchen above the countertop.... about 2 feet from that remote temp sensor sits my Keurig coffee maker... The heat off just brewing a fresh cup of coffee is just enough to make the remote sensor read a higher temp in the LR area ( where my zone 1 is ) and the furnace will shutdown way before the actual room temp I set on my CCC2 is met..

Example - while just up in YNP morning temps where 28 degrees... I bump the Tstat to 63 degrees when I get up and brew me a cup of coffee... Furnace is running, I get my coffee, sit down and furnace shuts down way before the actual air temp where I am sitting is 63 degrees ( verified with a stand alone thermometer )

Just offering up the above info and scenerio ... might be useful.. might not be...

Edited to Add: you may also have a Zone 1 remote temp sensor that is out of range of the resistance it should be reading for a given temp.... This can be measured up on the roof at the Zone 1 AC control box by removing the 2 wire remote temp sensor plug and put an ohmmeter across the plug and read the resistance...

Standard nominal readings you should read at a "Given" temp :

Ohm scale readings ….


The ohm reading for the remote sensor should be as follows: (+/- 10 Percent)

55 Degrees – 11667 ohms
60 Degrees – 10212 ohms
65 Degrees – 8959 ohms
70 Degrees – 7876 ohms
75 Degrees – 6939 ohms
80 Degrees – 6126 ohms
85 Degrees – 5418 ohms
90 Degrees – 4802 ohms
95 Degrees – 4264 ohms
100 Degrees – 3793 ohms
 
Last edited:
The Zone 1 roof AC unit control box is where the Furnace gets its signal to turn on from.... if the Tstat sends the signal to the control box then the two blue signal wires at the control box merely complete the connection at the furnace control board to run the blower and go thru start up sequence...

The CCC2 then looks at the Furnace set point temp versus the remote temp sensor for zone 1... if the temp is higher from Zone 1 remote sensor then Tstat set point furnace wont run...

How that remote temp sensor is mounted on the wall affects what actual ambient air temp the sensor sees.... if the sensor is sitting slightly inside the wall it cant sense accurate actual room air temp...

Resets and turning breakers off wont fix the issue you are seeing... looking at the location of that remote temp sensor for Zone 1 verus its placement on the wall will make a difference...

Example... my Zone 1 remote temp sensor is located in the kitchen above the countertop.... about 2 feet from that remote temp sensor sits my Keurig coffee maker... The heat off just brewing a fresh cup of coffee is just enough to make the remote sensor read a higher temp in the LR area ( where my zone 1 is ) and the furnace will shutdown way before the actual room temp I set on my CCC2 is met..

Example - while just up in YNP morning temps where 28 degrees... I bump the Tstat to 63 degrees when I get up and brew me a cup of coffee... Furnace is running, I get my coffee, sit down and furnace shuts down way before the actual air temp where I am sitting is 63 degrees ( verified with a stand alone thermometer )

Just offering up the above info and scenerio ... might be useful.. might not be...

Edited to Add: you may also have a Zone 1 remote temp sensor that is out of range of the resistance it should be reading for a given temp.... This can be measured up on the roof at the Zone 1 AC control box by removing the 2 wire remote temp sensor plug and put an ohmmeter across the plug and read the resistance...

Standard nominal readings you should read at a "Given" temp :

Ohm scale readings ….


The ohm reading for the remote sensor should be as follows: (+/- 10 Percent)

55 Degrees – 11667 ohms
60 Degrees – 10212 ohms
65 Degrees – 8959 ohms
70 Degrees – 7876 ohms
75 Degrees – 6939 ohms
80 Degrees – 6126 ohms
85 Degrees – 5418 ohms
90 Degrees – 4802 ohms
95 Degrees – 4264 ohms
100 Degrees – 3793 ohms
Thank you for the info, I will look at the AC area next
 
A few questions?

Are you the original owner of this camper? If so, did the furnace / AC work as expected in the past and then problems started recently?

Are you a 2nd or 3rd owner and have no history of the actual historic functionality of the camper (it's little quirks and quacks that all RV seems to have)?

If this is a new-to-you camper and if you have no prior experience with RV's, then rest assured, no 2 places inside the camper will have the same temperature, with either air conditioning or furnace heat. It all depends upon where the thermostat is set, potential drafts, other heated items that can affect the ambient temperature at the thermostat, and even time of day and season of year.

If this is a new-to-you camper there are a few items that should be "calibrated".

1) The thermostat actual setting and the actual temperature at the spot in the camper you spend the most time at.

2) The oven (if you have one). The dial on the oven showing the temperature settings mean absolutely nothing. The actual temperature inside the oven can be vastly different, and in an RV oven the top shelf can be 50 degrees different in temperature from the bottom shelf. Get yourself an oven thermometer and use it to calibrate the actual numbers on the knob.

3) Leveling the camper. Face it, there are no 2 spots on the camper that will show "level" at the same time. Floors, frame, cabinets, everything is not straight. Get the floor level, and the refrigerator could be completely kalli-whappered! Get the front door perfectly level and it does not swing open or shut, and the cabinet doors inside won't stay shut. In order to "level", you have to pick your spot in the camper that's most important and use that as the base line every time you level.

4) and #4.... the microwave oven. Not all microwave ovens are designed alike. Some have stronger power settings and some are weaker. If the package instructions say cook at High Temp for 10 minutes, that may be OK for one type of microwave, but in order to get the same results in another, it might require 13 minutes on High Temp.

So, this goes back to the furnace / AC thermostat, where is it physically located and how does the ambient temperature around it affect it's performance.

Also, if the thermostat is failing, replacing them is very simple. I've replaced both of mine (Dometic) just in the last year. They don't last forever. Click here.
 
A few questions?

Are you the original owner of this camper? If so, did the furnace / AC work as expected in the past and then problems started recently?

Are you a 2nd or 3rd owner and have no history of the actual historic functionality of the camper (it's little quirks and quacks that all RV seems to have)?

If this is a new-to-you camper and if you have no prior experience with RV's, then rest assured, no 2 places inside the camper will have the same temperature, with either air conditioning or furnace heat. It all depends upon where the thermostat is set, potential drafts, other heated items that can affect the ambient temperature at the thermostat, and even time of day and season of year.

If this is a new-to-you camper there are a few items that should be "calibrated".

1) The thermostat actual setting and the actual temperature at the spot in the camper you spend the most time at.

2) The oven (if you have one). The dial on the oven showing the temperature settings mean absolutely nothing. The actual temperature inside the oven can be vastly different, and in an RV oven the top shelf can be 50 degrees different in temperature from the bottom shelf. Get yourself an oven thermometer and use it to calibrate the actual numbers on the knob.

3) Leveling the camper. Face it, there are no 2 spots on the camper that will show "level" at the same time. Floors, frame, cabinets, everything is not straight. Get the floor level, and the refrigerator could be completely kalli-whappered! Get the front door perfectly level and it does not swing open or shut, and the cabinet doors inside won't stay shut. In order to "level", you have to pick your spot in the camper that's most important and use that as the base line every time you level.
or
4) and #4.... the microwave oven. Not all microwave ovens are designed alike. Some have stronger power settings and some are weaker. If the package instructions say cook at High Temp for 10 minutes, that may be OK for one type of micro6yrswave, but in order to get the same results in another, it might require 13 minutes on High Temp.

So, this goes back to the furnace / AC thermostat, where is it physically located and how does the ambient temperature around it affect it's performance.

Also, if the thermostat is failing, replacing them is very simple. I've replaced both of mine (Dometic) just in the last year. They don't last forever. Click here.
We are 2nd owners and had it 6yrs now. This problem is new this year. Thank you for the info, we are still trying to figure out why it will not come on at set thermostat temperature.
 