Furnace no run

Hi All,

2014 3150RL with a Dometic Comfort Control Center 2.

This morning turned on the LP furnace. The A/C fan came on. No furnace. Did the thermostat reset per instructions. No change.

It worked a month ago, but not now? Any ideas? Put it on AUTO, same thing.

Was 36 degrees outside this am, temp set @ 70.

Thanks Jim
 
__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Old 06-30-2013, 05:24 AM   #2
K0LCB
Montana Master
 
Join Date: Apr 2013
Location: Arroyo City
Posts: 3,110
M.O.C. #13395
Check your propane, turn burner on stove to see if it has air in line
K0LCB is offline   Reply With Quote
Old 06-30-2013, 05:34 AM   #3
jlb27537
Montana Master
 
Join Date: Jan 2013
Location: Depends on temps
Posts: 1,648
M.O.C. #13157
Water heater works, stove works, If you are out of LP the furnace blower will run but not ignite, after 3 attempts to light it will go into lock out and only the fan will run. Then you have to turn furnace off, and re-try.

The furnace fan never runs, instead the a/c fan runs.

Jim
__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Old 06-30-2013, 10:06 AM   #4
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
There is a re-boot you might have to do, but if we can't come up with that, kill the power to the A/C: Breaker, pull the fuse to the furnace, this is a hard reset, or re-boot, it may work then, I doubt the fan is bad with your new unit, BUT, you never know.
Ozz is offline   Reply With Quote
Old 06-30-2013, 12:54 PM   #5
jlb27537
Montana Master
 
Join Date: Jan 2013
Location: Depends on temps
Posts: 1,648
M.O.C. #13157
OZZ,

Turned battery switch off. Back on. Removed fuse to thermostat. Wait 60 sec. Re-install fuse. Kill breaker to A/C zone 1. Set thermostat to furnace. Nothing. Turn breaker on to A/C zone 1. A/C fan comes on.

Turn everything off. Remove furnace grill. Cut control wires to furnace. Connect 2 blue thermostat wires. Furnace runs and heats as normal. Re-connect control wires. No change.

Thermostat set to control furnace, A/C fan runs. Problem not furnace. Thermostat or control board in A/C defective?

Know how to check either? Have wiring diag for A/C and control board?

Maybe need some sort of reset for thermostat that is not in owners manual........

We have 2 elec heaters so will not freeze. 36 degrees this morning @ 9,400' with 50A service.

Life is good, furnace, not so good.

I'll call Dometic Monday.

Jim







__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Old 06-30-2013, 01:44 PM   #6
Rondo
Site Team
 
Join Date: Aug 2007
Location: Omaha
Posts: 6,796
M.O.C. #7560
Sounds like a trip to the dealer to have some warranty work done!
Rondo is offline   Reply With Quote
Old 07-01-2013, 02:25 AM   #7
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Cycle the thermostat to off..(No display) press and hold the + button first and without releasing it, press the On/Off button and hold. After a few seconds the display will indicate--, Release both buttons and then press on/off button to turn off the system. In the thermostat manual this is called the 'System Initialization' which should have been performed by the installer.
I don't have one of these, and am not familiar with your unit, so it may not apply, but heck, give it a try.
Good luck with it Jim.
Remember the old round Honeywell T87-f mechanical thermostats? Never a problem. Dang technology!
Glad you are having a good time and enjoying yourselves ..other than that.
Meanwhile, just turn the breaker off to the A/C unit, that will solve that problem.
Ozz
Ozz is offline   Reply With Quote
Old 07-01-2013, 03:41 AM   #8
jlb27537
Montana Master
 
Join Date: Jan 2013
Location: Depends on temps
Posts: 1,648
M.O.C. #13157
Ozz,

In the owners manual I have for the Comfort Control Center 2 which is the thermostat with the round display it says:

System Reset procedure:
1 Make sure CCC 2 thermostat is OFF
2 Press MODE and ZONE together. The LCD will display "IniT" and all available zones.
3 Release the MODE and ZONE buttons
4 Press the On/Off button to exit set up.

Is the instructions you gave me for the CCC 2 thermostat or for the old 4/5 button?

It used to work properly. So the dip switches are set properly and when you cycle thru the display it displays what is connected.

If I do not get any help from Dometic today I'll get a mechanical stat and wire it in and deal it when I get home. I am in the middle of Colorado on top of a 9,400' mountain and the closest place for parts is 100 miles over a 12K pass.

The A/C part of it works fine on both zones. The furnace on zone 1 is the only thing that does not work.

Jim
__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Old 07-01-2013, 03:56 AM   #9
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
There are installer set-up instructions and owner instructions, so they will be different. BUT I don't know which thermostat this is for, but it's all I have.
Ypou might try 'Google' and installer instructions for your thermostat.
Good call on the mechanical.
Ozz
Ozz is offline   Reply With Quote
Old 07-01-2013, 04:45 AM   #10
jlb27537
Montana Master
 
Join Date: Jan 2013
Location: Depends on temps
Posts: 1,648
M.O.C. #13157
Ozz, page 12 of 14

http://edometic.com/allusr/pdoc.nsf/...312792.017.pdf

Jim
__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace harrisje66 Additions & Improvements 11 04-28-2015 02:33 AM
Furnace Fan Blk_Adventurer General Discussions about our Montanas 4 03-29-2015 11:18 AM
Furnace K&Gs3400RL Montana Problems, Problem Solving & Technical Help 46 01-12-2012 02:00 AM
Furnace pdferg Maintenance 3 10-14-2007 04:04 AM
Furnace Montana_1973 Montana Problems, Problem Solving & Technical Help 1 08-17-2004 01:42 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:44 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.