Wiring problems
I found a couple of wiring issues in our 2003 montana 5ver. I could use some advice.
First, there are two separate breaker boxes. One box looks like where the power comes in. It has a 20 amp and 30 amp breaker for 50 amp service. The ground wires are badly burned in this box. Two of the white neutral wires have the insulation bubbled and scorched. I am not sure when in the past this happened, the trailer is new to us. Does anyone know what could have caused this? It seems to be still making a good ground and the power is strong and steady. Do I need to fix this, and if so how? Should there be enough extra cord that I can just cut off the wire and reconnect it? The hot wires look fine, and all the wiring in the second breaker box looks good.
My second problem is in my dc fuse box. One of the connections on one fuse is loose. If there is a fuse in it, it holds it in place, but if you take the fuse out, it looks like it has been touching the other side and bridging the gap. It looks a little burned. I also noticed that this connection is putting out slightly less voltage than the other fuses. For example if the others are putting out12.25v this one would be at 12.15v. Is this enough to cause an issue? Again, how would you fix this? Would the whole fuse board have to be replaced? I am not sure what this fuse goes to. It is possible it goes to some of my outside lights that are not working (I thought due to bulbs). I haven't gotten a chance to check this out yet.
|
|
|
10-19-2020, 08:49 AM
|
#2
|
Montana Master
Join Date: Dec 2009
Location: Sebring
Posts: 3,659
M.O.C. #9969
|
A few things: A 20 amp and 30 amp breaker does not make for a 50 amp service. A 50 amp service box has TWO 50 amp breakers.
Sounds like your unit might have been originally a 30 amp service that someone modified without really knowing what they were doing. The overheated wires are probably a result of running to many higher power appliances at the same time.
I think it's time to call in the Heavy Guns and get an Electrician to see exactly has been done.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
|
|
|
10-19-2020, 09:12 AM
|
#3
|
Seasoned Camper
Join Date: Aug 2020
Location: Edinburg
Posts: 88
M.O.C. #26856
|
[QUOTE=mhs4771;1201122]A few things: A 20 amp and 30 amp breaker does not make for a 50 amp service. A 50 amp service box has TWO 50 amp breakers.
The trailer has a 50 amp cord. As I understand it, One of the hot wires will power one breaker and the other hot wire will power the other breaker. The 20 amp breaker seems to controll the air conditioner. (There is only one.) The 30 amp breaker seems to carry everything else. The 20 and 30 amp breakers in the first box connect to a 30 and 30 amp breaker in the 2nd box. The 30 amp then powers 4 15 amp breakers which did confuse me because that equals 60 amps. The only heavy draw item we will be using is the microwave.
|
|
|
10-19-2020, 09:16 AM
|
#4
|
Seasoned Camper
Join Date: Aug 2020
Location: Edinburg
Posts: 88
M.O.C. #26856
|
I hope these are the right pictures
|
|
|
11-04-2020, 02:05 PM
|
#5
|
Montana Master
Join Date: Jun 2020
Location: Qualicum Beach
Posts: 665
M.O.C. #26399
|
Quote:
Originally Posted by dallasrules
I hope these are the right pictures
|
I AM AN ELECTRICIAN
Please unplug that trailer NOW and get an electrician to fix it. The RV is a 30 amp RV. That means 30 amps TOTAL. A 50 amp RV is 50+50. Sadly the RV industry did a stupid thing calling it 50,it's actually 100Amps total.
The wiring shows significant overloading and will need some wire replacement, removing the unsafe and illegal modifications made to return the RV to a 30A RV. If anything happens that injures another party, since you have been advised the RV is dangerous you would be criminally liable. VERY different penalties, jail time not fines.
__________________
2018 Keystone Montana 3811MS
2017 Ford F450 diesel dually
600AH Battle Born Lithium Batteries, 1,080 watts solar
3,000 watt hybrid inverter with 120A charger
|
|
|
11-04-2020, 06:12 PM
|
#6
|
Montana Fan
Join Date: Mar 2016
Location: Austin
Posts: 226
M.O.C. #18363
|
Quote:
Originally Posted by dallasrules
I hope these are the right pictures
|
Dallas,
Those look like two circuits. Or maybe a service feed and one circuit. Hard to tell from the pics. The black, white and green/copper wires will go to the same circuit.
Looks like they have been overloaded, which will cause them to burn.
I would trace them to see where they go. That will also help you determine if it's two circuits or 1 and a service feed. They should be replaced anyhow. You can look up some charts online to help you properly size the replacement 8/10/12 gauge wire. Size them to the 20 amp or 30 amp breakers accordingly.
To trace a wire you can physically follow it from end to end, or you can use a voltmeter to check continuity or just flip switches/breakers until you can see what turns on/off.
The hots (black wire) will go through each breaker. The neutral (white wire) will go to the buss bar and the grounds ( green/copper) will go to a ground bar.
Typically, your service feed will come into the box and wire to each of those bars and the hot will go to your main breaker (30 amp). Everything feeds from there.
Get yourself a voltmeter so you can check continuity and power.
|
|
|
10-19-2020, 09:14 AM
|
#7
|
Montana Master
Join Date: Dec 2007
Location: Kansas City, Missouri
Posts: 2,707
M.O.C. #7992
|
Quote:
Originally Posted by mhs4771
A few things: A 20 amp and 30 amp breaker does not make for a 50 amp service. A 50 amp service box has TWO 50 amp breakers.
Sounds like your unit might have been originally a 30 amp service that someone modified without really knowing what they were doing. The overheated wires are probably a result of running to many higher power appliances at the same time.
I think it's time to call in the Heavy Guns and get an Electrician to see exactly has been done.
|
If you are not real savvy on electrical she is giving you some really good advice!
__________________
2006 3000RK
2009 Ram 2500
|
|
|
11-04-2020, 05:47 PM
|
#8
|
Montana Fan
Join Date: Mar 2016
Location: Austin
Posts: 226
M.O.C. #18363
|
Quote:
Originally Posted by mhs4771
A few things: A 20 amp and 30 amp breaker does not make for a 50 amp service. A 50 amp service box has TWO 50 amp breakers.
Sounds like your unit might have been originally a 30 amp service that someone modified without really knowing what they were doing. The overheated wires are probably a result of running to many higher power appliances at the same time.
I think it's time to call in the Heavy Guns and get an Electrician to see exactly has been done.
|
My public math education said 20 + 30 = 50. So it "could" be a single leg 50 amp service. You can run up to 50 amps on a single leg of service.
50 amp service today is generally two legs of 50 amp service, which can support 100amps.
|
|
|
10-19-2020, 10:05 AM
|
#9
|
Montana Fan
Join Date: Jul 2015
Location: Edgerton
Posts: 218
M.O.C. #17678
|
Wow. Just wow. Whoever has been messing around in that unit should be taken out in the middle of the street & put out of their misery before they kill someone else. Nothing about that wiring is right. It all needs to be ripped out & start over.
|
|
|
10-19-2020, 10:13 AM
|
#10
|
Montana Master
Join Date: Dec 2009
Location: Sebring
Posts: 3,659
M.O.C. #9969
|
It's easy to change the socket on the RV from 30 to 50, BUT adding a 20 & 30 amp breakers DOES NOT make a 50 amp service. Look at the Park electric pole where you plug in, for the 50 amp plug you'll see TWO 50 amp breakers and a TRUE 50 amp RV's power panel will also have two 50 amp breakers.
The previous owner modified that unit and did a really Half A** job of it and it looks pretty darn dangerous to me, I would be afraid to connect power to it.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
|
|
|
10-19-2020, 10:20 AM
|
#11
|
Site Team
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,369
M.O.C. #4831
|
I believe in 2003 (and earlier) the Montanas had a 50 amp service comprised of a 30 amp and a 20 amp set of breakers. It wasn't until later a "true" 50 amp (actually 100 amp) service was introduced. Finding someone with this setup is getting harder all the time. PM member Drifty1 as he has a 2002 and is *VERY* handy with all thing Montana.
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB
|
|
|
10-31-2020, 06:31 PM
|
#12
|
Seasoned Camper
Join Date: Aug 2020
Location: Edinburg
Posts: 88
M.O.C. #26856
|
Quote:
Originally Posted by Carl n Susan
I believe in 2003 (and earlier) the Montanas had a 50 amp service comprised of a 30 amp and a 20 amp set of breakers. It wasn't until later a "true" 50 amp (actually 100 amp) service was introduced. Finding someone with this setup is getting harder all the time. PM member Drifty1 as he has a 2002 and is *VERY* handy with all thing Montana.
|
Thanks. Will do
|
|
|
10-19-2020, 10:49 AM
|
#13
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,170
M.O.C. #6433
|
Those two white discolored white wires obviously show signs of overheating. And by the way the insulation melted, they overheated at the end where they connect to the buss bar indicating a poor connection there. Poor connection equals resistance and that along with current results in heat. And the larger wire also has corrosion on it.
You might be able to pull the larger wire on the right in a little to gain some length, then cut off the end of the white wire, and reconnect it to one of the lugs to the right making sure it is tight.
It would be good if you could also pull the smaller white wire on the left in a little, but it does not appear corroded like the other, so you might just clean it and reinsert it and make sure it is tight. That screw is not in nearly as far as the white wire next to it indicating it is not as tight. You could also put some shrink tubing on it to cover the bare section.
The difference in the voltage on the 12 volt fuse is small, but might also indicate a poor connection for the fuse holder. Again, poor connection equals heat. And in the worst case, potential for fire. If you do not have any spare fuse spaces that you can move that wire to, then you might need to replace that board. Pictures?
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
10-31-2020, 05:37 PM
|
#14
|
Montana Fan
Join Date: Jul 2020
Location: ladson,SC
Posts: 201
M.O.C. #26644
|
i have seen that "WIRE BURN" in my business many times. (your white). It starts as a loose connection which generates heat at the source of the connection....
The main problem... (not the insulation ) is when the copper changes to that BURNT look then the current carrying capacity of the wire diminishes . If it ever heats to the point of break off (no load capable) the voltage on your 120 volt appliances will go to 240 volt and BURN up everything electrical.
Weather you trailer started as a 30 amp and was modified to handle a 50 amp load or if it just came that way.....
YOU MUST ELIMINATE THAT BURNT WHITE WIRE.....do what ever you have to do to cut back about 6" both the 2-black and white wire.....do not take this lightly. Re attach to terminals that are not burnt.... if the circuit breaker has a burn terminal replace with new they are cheap enough.
as far as you 12 volt fuse problem ..can not comment till i see a photo
|
|
|
10-31-2020, 06:30 PM
|
#15
|
Seasoned Camper
Join Date: Aug 2020
Location: Edinburg
Posts: 88
M.O.C. #26856
|
YOU MUST ELIMINATE THAT BURNT WHITE WIRE....
I will work on this. If there isn't any slack, can I run these into a junction box and connect to new wire to run to the bus? Or can I run them to a bus in a junction box and the run a heavier guage ground wire from the new bus to the old bus?
|
|
|
10-31-2020, 08:33 PM
|
#16
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,170
M.O.C. #6433
|
Quote:
Originally Posted by dallasrules
YOU MUST ELIMINATE THAT BURNT WHITE WIRE....
I will work on this. If there isn't any slack, can I run these into a junction box and connect to new wire to run to the bus? Or can I run them to a bus in a junction box and the run a heavier guage ground wire from the new bus to the old bus?
|
If the wires will not pull thru those fittings, there may be a clamp on the other side.
Looks like that ground wire was twisted inside a wire nut at one time.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
11-01-2020, 02:40 PM
|
#17
|
Montana Fan
Join Date: Jul 2020
Location: ladson,SC
Posts: 201
M.O.C. #26644
|
Quote:
Originally Posted by dallasrules
YOU MUST ELIMINATE THAT BURNT WHITE WIRE....
I will work on this. If there isn't any slack, can I run these into a junction box and connect to new wire to run to the bus? Or can I run them to a bus in a junction box and the run a heavier guage ground wire from the new bus to the old bus?
|
that ground wire looks like it was clamped into the ground buss before.
you don't need to change to heaver wire when splicing because a chain is only as heavy as the weakest link....
if you run a new wire to splice in make sure you TWIST the wires together BEFORE you insert into a wire nut
|
|
|
11-04-2020, 02:12 PM
|
#18
|
Montana Master
Join Date: Jun 2020
Location: Qualicum Beach
Posts: 665
M.O.C. #26399
|
Quote:
Originally Posted by ForBruce
i have seen that "WIRE BURN" in my business many times. (your white). It starts as a loose connection which generates heat at the source of the connection....
The main problem... (not the insulation ) is when the copper changes to that BURNT look then the current carrying capacity of the wire diminishes . If it ever heats to the point of break off (no load capable) the voltage on your 120 volt appliances will go to 240 volt and BURN up everything electrical.
Weather you trailer started as a 30 amp and was modified to handle a 50 amp load or if it just came that way.....
YOU MUST ELIMINATE THAT BURNT WHITE WIRE.....do what ever you have to do to cut back about 6" both the 2-black and white wire.....do not take this lightly. Re attach to terminals that are not burnt.... if the circuit breaker has a burn terminal replace with new they are cheap enough.
as far as you 12 volt fuse problem ..can not comment till i see a photo
|
Electrician here. I know of no way to get 240V on any appliance in an RV without connecting the appliance to the 2 hot legs. A neutral (white wire) breaking off will cause 0 Volts on that entire circuit.
__________________
2018 Keystone Montana 3811MS
2017 Ford F450 diesel dually
600AH Battle Born Lithium Batteries, 1,080 watts solar
3,000 watt hybrid inverter with 120A charger
|
|
|
11-04-2020, 03:39 PM
|
#19
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,170
M.O.C. #6433
|
Quote:
Originally Posted by bcrvman
Electrician here. I know of no way to get 240V on any appliance in an RV without connecting the appliance to the 2 hot legs. A neutral (white wire) breaking off will cause 0 Volts on that entire circuit.
|
Actually being a 120/240 split phase power system, it depends on where the neutral was broken, and whether two devices were each connected to a different hot, and on whether those two devices were both turned on.
Looking at the pictures, if one of the neutral wires on the left side of the neutral buss lost continuity with the buss bar, then there would be zero volts on the device(s) connected to it. But if the neutral wire on the right side of the buss bar (the source neutral) were broken, and the neutrals on the left still intact, and there were two devices with each one connected to a different hot, and both were turned on, then there would be 240 vac across those two devices since they would effectively be connected in series to the two hots. The neutral buss bar would be floating. The actual voltage applied to each individual device would be dependent on the impedance of each, not 240 vac to each.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
11-04-2020, 05:33 PM
|
#20
|
Established Member
Join Date: Jun 2019
Location: Fruitland park
Posts: 13
M.O.C. #24308
|
Most rv 30 amp breakers are 120
Same as 20 amp. Looks like half the box is 30 the other 20. 50 amp rv is a 240 that needs both legs
|
|
|
|
|