Need Data: Trailer not receiving gen pwr

I need a big favor.
Problem:
I have a 2021 Montana 3120RL with Super Solar Flex. When I connect any generator the Power Control System Central Monitor display shows a reading of 65V on Line 1 & Line 2. The reading should be normal 115V.
Discussion:
I'll spare you all the trouble shooting effort that continues for my trailer. It would make this post way too long. The good folks at Keystone picked it up last Fall and are still having trouble with it. I'd like to survey this group and see if any one else is experiencing this issue.
Favor:
We need some data.
1. Does anyone else have a similar reading with similar trailer?
With your gen connected do you get 65V vice 115V?
2. Does anyone else have a normal reading with similar trailer?
With your gen connected do you get 115V? If yes, what model gen is it?

Thanks so much for your input!
 
Hazex4 is offline   Reply With Quote
Old 03-25-2022, 10:41 AM   #2
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,695
M.O.C. #24086
Have a look at this thread.

https://www.montanaowners.com/forums...ight=Generator
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
Daryles is offline   Reply With Quote
Old 03-25-2022, 02:39 PM   #3
Carl n Susan
Site Team
 
Carl n Susan's Avatar
 
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,366
M.O.C. #4831
Quote:
Originally Posted by Daryles View Post
I thought the same thing - I have read about this before. And I had. That Thread was created by Hazex4 who is also the creator of this Thread.So that other Thread doesn't seem to answer his questions.
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB

Carl n Susan is offline   Reply With Quote
Old 03-26-2022, 08:43 AM   #4
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
Thanks Daryles and Carl. That's my original post in Jan, your trouble shooting ideas were great but no luck. I'm desperately trying to find out who else is having this issue hence the data request. I'd really like to hear from someone who has the Super Solar Flex option on their Montana and is able to use their generator as well. By this I mean their PCS display shows normal 115V instead of 65V and no Brown Out. Likewise anyone who has the same problem I do. I can't be the only guy with this issue!!
Thanks again,
Brad
Hazex4 is offline   Reply With Quote
Old 03-26-2022, 09:31 AM   #5
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
To all, please feel free to send me a private message.
Thanks,
Brad
Hazex4 is offline   Reply With Quote
Old 03-26-2022, 09:50 AM   #6
RipNC
Montana Fan
 
Join Date: Aug 2020
Location: Aurora
Posts: 429
M.O.C. #26926
Sounds like floating neutral issue that is not uncommon with portable generators. Google your generator model along with "floating neutral".
__________________
Rip & Beth
2021 3121RL Legacy Cobalt FBP, MORryde IS & pin box
2020 F350 PSD CCLB SRW
RipNC is offline   Reply With Quote
Old 03-27-2022, 08:46 AM   #7
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
Thanks RipNC. I wish that was the problem but it was ruled out early in the trouble shooting. I've tried several generators since and different methods of grounding. No luck. The dealership did their best and now it's back at the factory in Goshen. I gotta believe someone out there is having the same problem.
Hazex4 is offline   Reply With Quote
Old 03-27-2022, 09:06 AM   #8
RipNC
Montana Fan
 
Join Date: Aug 2020
Location: Aurora
Posts: 429
M.O.C. #26926
Quote:
Originally Posted by Hazex4 View Post
Thanks RipNC. I wish that was the problem but it was ruled out early in the trouble shooting. I've tried several generators since and different methods of grounding. No luck. The dealership did their best and now it's back at the factory in Goshen. I gotta believe someone out there is having the same problem.
Long way to go for an electrical exorcism... Let us know what the final diagnosis is!
__________________
Rip & Beth
2021 3121RL Legacy Cobalt FBP, MORryde IS & pin box
2020 F350 PSD CCLB SRW
RipNC is offline   Reply With Quote
Old 03-27-2022, 09:09 AM   #9
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
Ha...believe me that wasn't the only problem!! Good news is Keystone is trying to make it right.
Hazex4 is offline   Reply With Quote
Old 03-27-2022, 09:13 AM   #10
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,695
M.O.C. #24086
Ok you have the factory installed super solarflex package. I'm guessing it has a built in EMS and transfer switch.
Any chance you could bypass the EMS to see it it will take power?
If it does have the factory installed transfer switch,
That's a Progressive Dynamics Automatic transfer switch. They have had a lot of trouble with them lately and I believe they were recalled.
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
Daryles is offline   Reply With Quote
Old 03-27-2022, 09:51 AM   #11
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
You are correct Daryles. The transfer switch has been replaced, however, I don't think the EMS has been bypassed. My post title is misleading: "Trailer not receiving gen pwr". Actually it's not receiving proper power. The read out on the PCS display is 65V instead of 115V and I get a Brown Out warning. This can damage any AC system if you try to operate one, ie microwave, air cond etc. I'll certainly pass on your suggestion to the Keystone Techs on bypassing the EMS. You can charge batteries with the gen but the inverter has to be off. Otherwise the trailer may go dark. I've asked the Keystone Tech to check proper installation of the inverter as far as grounding. The manual is very specific on installation. I'd really like to know if anyone else has this issue or what generator they're using if they don't!
Hazex4 is offline   Reply With Quote
Old 03-27-2022, 03:42 PM   #12
Arkware
Montana Master
 
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
I have supersolar and experienced the exact issue.
The fix was a bonding plug, plugged into the generator.

A bonded plug ties the neutral and ground.
Arkware is offline   Reply With Quote
Old 03-27-2022, 05:05 PM   #13
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
Thanks Arkware. I bought 2 Ground Neutral Plugs, one for each of my Honda 2000's. I also used my neighbors 4000W gen with no help. What generator are you using?
Hazex4 is offline   Reply With Quote
Old 03-27-2022, 07:29 PM   #14
Arkware
Montana Master
 
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
I have a champion 3400.
Another MOC member has 2 Hondas.
We both need the bonding plug.

I think it's pretty standard that inverter generators have a floating ground.

Thank goodness we have Montana s with PCS.
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
Arkware is offline   Reply With Quote
Old 04-01-2022, 12:08 PM   #15
Greg n Tracy
Established Member
 
Join Date: May 2019
Location: council bluffs
Posts: 40
M.O.C. #24154
I do not have the Super Solar, just the smaller solar flex, but I did replace the progressive dynamics transfer/surge with the watchdog surge and dedicated PD transfer. When I parallelled my two Honda 2200's, it would shut the surge protector down. I tried first one and then two of the grounded plugs, to no avail. Then I switched the two parallel wires around on the gennys, with one grounding plug, and that was the trick. No problems since. Maybe this will help. Good luck.
Greg n Tracy is offline   Reply With Quote
Old 04-01-2022, 12:22 PM   #16
Hazex4
Established Member
 
Join Date: Aug 2020
Location: Reno
Posts: 13
M.O.C. #26860
Thanks Greg! I will try switching the parallel wires and see if that works. Can you connect a single Honda Gen without problems?
Hazex4 is offline   Reply With Quote
Old 04-01-2022, 08:31 PM   #17
rames14
Montana Master
 
rames14's Avatar
 
Join Date: Aug 2004
Location: Livermore
Posts: 5,146
M.O.C. #1920
Brad, ours works fine with one or two Honda 2000’s. You only need one bonding plug on one of the Honda’s. Once the neutral and ground are bonded, it will be the same through the system. Good luck testing the systems.
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
rames14 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 11:17 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.