in Command CM replacement or repair

Had trouble closing my living room slides this weekend and after exstensive troubleshooting I have it narrowed down to a either an issue with the HMI inside or a bad output point on the CM. The coil test and works fine on the solenoid and the wires ohm good from the CM. Also tested the relay which is good.

When you fire the Hydralic room at the HMI , the HMI disconnects and goes through a reconnect status then comes back on. This also happens withe the wires lifted at the CM for the solenid and the relay removed.

Does anyone know where I can get an elementary drawing for the HMI and CM?

I can't find the output that fires the reversing contactor for the hydralic pump to eliminate that output as a problem.



Also it would not operate in manual on the board.
 
dbcustom is offline   Reply With Quote
Old 10-25-2021, 08:32 AM   #2
ChuckS
Montana Master
 
Join Date: Dec 2017
Location: Mountain Home
Posts: 839
M.O.C. #20949
I doubt you will get a schematic for the BCM or the DC... what version of In command are you using?

ProPlus JVRCS2?
PRO JVRCS105?
Gen 1.0 JVRCS1?

or latest Global connect NCSP3 or NCSP35?
ChuckS is offline   Reply With Quote
Old 10-25-2021, 08:36 AM   #3
ChuckS
Montana Master
 
Join Date: Dec 2017
Location: Mountain Home
Posts: 839
M.O.C. #20949
Also you realize that NOT ONLY must the dual polarity solenoid get a "12 volt DC signal) at either extend or retract terminal .. the HYDAC valve for the hydraulic slides (only one) has to also receive 12 volts DC to its coil to energize the solenoid on the slide out HYDAC and open it for fluid flow to occur
ChuckS is offline   Reply With Quote
Old 10-25-2021, 08:37 AM   #4
dbcustom
Established Member
 
Join Date: Apr 2017
Location: Addis
Posts: 15
M.O.C. #19738
Gen 1.0 JVRCS1
dbcustom is offline   Reply With Quote
Old 10-25-2021, 08:43 AM   #5
dbcustom
Established Member
 
Join Date: Apr 2017
Location: Addis
Posts: 15
M.O.C. #19738
I was able to use the wires from the left jack solenoid and close the slide so I know the valve is working. But I can't locate the output that fires the reversing contactor for the pump. The wire are doubled at the coil on the contactor so I figure on set is from the leveling panel and the other is from the BCM
dbcustom is offline   Reply With Quote
Old 10-25-2021, 08:51 AM   #6
ChuckS
Montana Master
 
Join Date: Dec 2017
Location: Mountain Home
Posts: 839
M.O.C. #20949
One set of wires on extend and retract sides of dual polarity solenoid is for slide outs and other is for level up system…

That’s an old BCM so you may have troubles getting a new replacement

Pin out of BCM which you probably already have
Attached Thumbnails
Click image for larger version

Name:	F2AA8551-9564-40A0-8C68-3129888456A0.jpg
Views:	65
Size:	180.6 KB
ID:	10449  
ChuckS is offline   Reply With Quote
Old 10-25-2021, 08:53 AM   #7
ChuckS
Montana Master
 
Join Date: Dec 2017
Location: Mountain Home
Posts: 839
M.O.C. #20949
Since you know the Hydac is working did you try removing wires from Hydac output on the BCM and try operating from the display panel to see if it disconnects still?

You may have a short or open on those two wires
ChuckS is offline   Reply With Quote
Old 10-25-2021, 08:58 AM   #8
ChuckS
Montana Master
 
Join Date: Dec 2017
Location: Mountain Home
Posts: 839
M.O.C. #20949
Probably your best bet is to call ASA Jensen In Command Tech support and they may be able to further assist you... may be tough getting a new panel if its smoked
ChuckS is offline   Reply With Quote
Old 10-25-2021, 08:58 AM   #9
dbcustom
Established Member
 
Join Date: Apr 2017
Location: Addis
Posts: 15
M.O.C. #19738
Can the BCM and DC be purchased not going through a dealer if it's the problem? Just thinking ahead, but I have heard so many horror stories I have reapired everything on my Montana since day one.
dbcustom is offline   Reply With Quote
Old 10-25-2021, 09:00 AM   #10
dbcustom
Established Member
 
Join Date: Apr 2017
Location: Addis
Posts: 15
M.O.C. #19738
Perfect thats what i was looking for , I had the valve output but not the motor. I will get back on it when I get home.

Thanks
dbcustom is offline   Reply With Quote
Old 10-25-2021, 09:02 AM   #11
dbcustom
Established Member
 
Join Date: Apr 2017
Location: Addis
Posts: 15
M.O.C. #19738
I will keep you posted.

Thanks for the help
dbcustom is offline   Reply With Quote
Old 10-25-2021, 09:11 AM   #12
ChuckS
Montana Master
 
Join Date: Dec 2017
Location: Mountain Home
Posts: 839
M.O.C. #20949
Worst case if you cant repair the BCM .. if thats the issue is you could install a separate momentary on dual pole switch to handle the outputs for 12 volts to both the HYDAC valve and dual polarity solenoid Extend/Retract terminals on the solenoid
ChuckS is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 06:15 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.