Had trouble closing my living room slides this weekend and after exstensive troubleshooting I have it narrowed down to a either an issue with the HMI inside or a bad output point on the CM. The coil test and works fine on the solenoid and the wires ohm good from the CM. Also tested the relay which is good.
When you fire the Hydralic room at the HMI , the HMI disconnects and goes through a reconnect status then comes back on. This also happens withe the wires lifted at the CM for the solenid and the relay removed.
Does anyone know where I can get an elementary drawing for the HMI and CM?
I can't find the output that fires the reversing contactor for the hydralic pump to eliminate that output as a problem.
Also it would not operate in manual on the board.