Mike my Xantrex manual says 250A max and min 2/0 wire.
That would be correct. The fuse is sized from the wire size per table 310-16 of the national electric code. It is not based upon the battery size or capacity. The fuse size is meant to protect the 2/0 wire’s ampacity.