View Single Post
Old 08-16-2019, 04:58 PM   #3
Lucky23
Montana Fan
 
Lucky23's Avatar
 
Join Date: Nov 2015
Location: Shady Cove
Posts: 154
M.O.C. #18031
Quote:
Originally Posted by PNW Fireguy View Post
I believe that your wire is oversized for your inverter but that is not a problem. I would not change that because it will lesson any voltage drop effect. The catastrophic fuse is sized to protect the wire. A class T 400A fuse would be correct for 4/0 wire however you could reduce that size down to 250A and be fine because you will probably never get 400 amps out of your pack. Whatever you decide buy more than one.
Thanks Fireguy,
So it would be ok to use 2/0 and drop the fuse down to 250A.
Also can I still go with the Victron battery moniter system w/ 500A shunt?
Lucky23 is offline   Reply With Quote