quote:Originally posted by H. John Kohl


The plug OVERLORD showed is an adition plug that is plugged into the generator, either the other 15 amp socket or the 15 amp socket when using the 30 amp socket.
The orange plug makes the generator have a neutral (the larger lug of the plug) and ground tied together. This satisifies the EMS.

I hope this helps and great questions.
Okay, I think I have it. I know the stick house and RV campground normally have both the neutral and frame ground shorted per the code in the panel box. Apparently the generator from Honda does not. So all I do is take my Montana 50 amp cord protected by PI EMS and plug it into which every adapter I want to us to connect to the Honda 2000UI/Companion paralleled; 30 amp or 15 amp. Then I plug in my "special" orange plug into the other 15 amp plug. And all the orange plug has wired is frame ground to white.