Not to code... you need the linked 50 amp primary breakers. The breaker box you have now has conductors in it rated for 30 amps not 50. No point in buying insurance cause if you have any sort of fire and they look at that wireing.....Then if you ever sell it an the next guy has a problem....Sounds like your spending a lot to get very little, other then increased personal liability.

By the way... why not save yourself a bit of money. Were here in a 3670 with washer dryer hooked up to 30 amps. Been here almost two months. We can operate washer, air and normal loads no sweat. The washer dryer only draws 15amps, they are not the 30amp household variety.

But...I guess if we really need the hair dryer... we may have to turn something off....