Almost had an electrical fire

I have a 2017 Montana 3160RL Legacy Edition that I purchased new. Recently it almost caught on fire.

My RV has had minimal use. We park it in an RV park near a lake that only has 30amp service to sites so we always use only one air conditioner. I also installed a Progressive Industries hard wire surge protector before we took delivery of our new RV.

Recently I lost power to the RV and couldn't find out why as everyone around us had power.

I called a mobile RV repair tech and he discovered the the shore power female plug-in at the rear of the trailer had arced because of loose connections on the rear of the plug.

The only plausible conclusion was they were loose from the factory. The rear of the plug was burnt up.

The RV tech said we almost had a fire. I suggest you check your plugs.

I'm not happy with Montana.
 
johnregrus is offline   Reply With Quote
Old 08-21-2019, 04:00 PM   #2
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
The is a fairly common issue and the plug should be checked and replaced with a 90 degree plug.They take a lot of stress over time being plugged straight in
richfaa is offline   Reply With Quote
Old 08-21-2019, 09:43 PM   #3
rohrmann
Montana Master
 
rohrmann's Avatar
 
Join Date: Oct 2012
Location: Box Elder
Posts: 4,690
M.O.C. #12947
If you had loose connections at the receptacle at the rear of your rig, they probably weren't loose from the factory, but with use and electrical loading, the connections will get loose as load means heat, and when you heat a connection and then it cools, there is expansion when hot, and when it cools, the wire and connectors shrink, and there you have loose connections. You should check every connection you can access in your rig, maybe annually, but at least once after you have had your rig a while, and this also means 120 volt as well as 12 volt connections, especially in the main panel of the rig.


When you are connected to a 30 amp service, you are loading up close to the max of 30 amps, so you will see lower voltage which means higher amperage and that is heat, where with a 50 amp service, you will rarely load either leg even close to it's max load, so you don't get the connections as hot. Whenever it's possible, try to get 50 amp service so things are easier on your rig's electrical system.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
rohrmann is offline   Reply With Quote
Old 08-24-2019, 06:37 AM   #4
mootana
Montana Fan
 
Join Date: Oct 2014
Location: Monroe
Posts: 183
M.O.C. #15746
Well said!
__________________
DBA Samtana
mootana is offline   Reply With Quote
Old 08-25-2019, 10:06 PM   #5
DmaxDually
Montana Fan
 
Join Date: Mar 2014
Location: New Port Richey
Posts: 438
M.O.C. #14092
I never stay at a sight or camp ground that only has 30 amp service.
__________________
2012 Silverado 3500HD|4x4|Crew Cab|long bed|Dually
2012 Montana 3750FL
DmaxDually is offline   Reply With Quote
Old 08-26-2019, 07:44 AM   #6
SteveandTerri
Seasoned Camper
 
Join Date: Jul 2018
Location: Vacaville
Posts: 81
M.O.C. #22227
Main Electrical Power Receptacle: Poor Terminations

The wires that were connected to the electrical receptacle may not have been terminated properly. Here's a thread that may apply:

https://www.montanaowners.com/forums...ad.php?t=78383
__________________
Steve & Terri
2017 305RL Montana High Country
2017 F-250 CCSB Diesel Lariat FX4
SteveandTerri is offline   Reply With Quote
Old 08-26-2019, 08:52 AM   #7
NCFischers
Montana Master
 
Join Date: Aug 2008
Location: New Bern
Posts: 4,370
M.O.C. #8728
Send a message via Yahoo to NCFischers
The power cords are bought in bulk from another manufacturer by Montana and placed in the RV still wrapped up. Your anger is misplaced.
NCFischers is offline   Reply With Quote
Old 08-26-2019, 08:59 AM   #8
SteveandTerri
Seasoned Camper
 
Join Date: Jul 2018
Location: Vacaville
Posts: 81
M.O.C. #22227
In my case, the cord wasn't the problem. One of the power leg wires was inserted too far such that the wire's insulation was under the clamp.
__________________
Steve & Terri
2017 305RL Montana High Country
2017 F-250 CCSB Diesel Lariat FX4
SteveandTerri is offline   Reply With Quote
Old 09-01-2019, 01:18 PM   #9
deansue1
Established Member
 
Join Date: Jan 2019
Location: Green Cove Springs
Posts: 14
M.O.C. #23342
Had the same problem with my unit and I was plugged into a 50amp plug found camper was missed wired on my 2018. The plug on the cord and camper were welded together.
deansue1 is offline   Reply With Quote
Old 09-01-2019, 03:07 PM   #10
Nat_Park_Travelers
Seasoned Camper
 
Join Date: Jun 2018
Posts: 70
M.O.C. #21914
We just went through the same thing with our 2019 3700LK - lost power after a week of being plugged in. I went outside and the outlet was smoking big-time. I pulled the plug from the shore post, disconnected from the trailer, shut off all breakers and got my screw gun and removed the outlet from the trailer. Mechanic said it was loose connection that arced, and yes, likely from the factory. Didn't make any sense why after being plugged into the same post for a week all of a sudden the outlet melted and started smoking. The PD EMS didn't even catch it, I guess because it was at the outlet before getting to the EMS and was already off.
Nat_Park_Travelers is offline   Reply With Quote
Old 09-02-2019, 08:33 AM   #11
Mark N.
Montana Master
 
Join Date: Oct 2013
Location: Ogden
Posts: 638
M.O.C. #13862
Quote:
Originally Posted by DmaxDually View Post
I never stay at a sight or camp ground that only has 30 amp service.
Care to explain why? I've done so many, many times without issue. There's no risk in using an adapted 30A pedestal. You are simply restricted to one A/C unit.
Mark N. is offline   Reply With Quote
Old 10-04-2019, 05:41 AM   #12
margerush
Montana Fan
 
margerush's Avatar
 
Join Date: Oct 2017
Location: Riverview
Posts: 178
M.O.C. #20713
richfaa--I want a 90 degree dog bone but can't find one. I bought & returned one from etrailer. The 90 hung to the side (not down) & needed to be twisted to the right, therefore, the weight of my power cord pulled it down & made a bad connection. Please suggest who I can get a good 90 degree perpendicular to the ground.
__________________
traded 2016 Montana and 2016 2500 RAM mega cab for
2020 Gulf Stream Conquest Class C on
Ford E-450 frame
Toad: 2017 Jeep Wrangler
margerush is offline   Reply With Quote
Old 10-04-2019, 06:37 AM   #13
SteveandTerri
Seasoned Camper
 
Join Date: Jul 2018
Location: Vacaville
Posts: 81
M.O.C. #22227
Main Electrical Power Inlet Receptacle in the Back of your 5er

Margerush: "I want a 90 degree dog bone but can't find one. I bought & returned one from etrailer. The 90 hung to the side (not down) & needed to be twisted to the right, therefore, the weight of my power cord pulled it down & made a bad connection. Please suggest who I can get a good 90 degree perpendicular to the ground."

I ran into the same thing. I had to disassemble and rotate the Main Electrical Inlet Socket (the receptacle that's built in to the back of the rig, where you insert your power cord) so that the cord would hang straight down. Seems the Keystone technician that attached the wires to the socket rotated that part of the assembly 120 degrees when they put it back together.

(Note: The socket has to be partially disassembled in order to terminate wires to it. When it was wired for the first time - at Keystone - it was assembled such that the internal component was 120 degrees from where it should have been.)

fyi: Before I figured this out, I also returned a 90 degree cord adapter to etrailer thinking it was defective...
__________________
Steve & Terri
2017 305RL Montana High Country
2017 F-250 CCSB Diesel Lariat FX4
SteveandTerri is offline   Reply With Quote
Old 10-04-2019, 07:04 AM   #14
DmaxDually
Montana Fan
 
Join Date: Mar 2014
Location: New Port Richey
Posts: 438
M.O.C. #14092
Quote:
Originally Posted by Mark N. View Post
Care to explain why? I've done so many, many times without issue. There's no risk in using an adapted 30A pedestal. You are simply restricted to one A/C unit.
Yes, I don't want to be restricted to one A/C unit or having to worry about power management. I don't want to have to turn things off so I can use something else.
__________________
2012 Silverado 3500HD|4x4|Crew Cab|long bed|Dually
2012 Montana 3750FL
DmaxDually is offline   Reply With Quote
Old 10-04-2019, 08:03 AM   #15
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
My 3402 was proper from the factory got the dog bone from CW.
richfaa is offline   Reply With Quote
Old 10-04-2019, 08:49 AM   #16
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,156
M.O.C. #6433
Quote:
Originally Posted by DmaxDually View Post
I never stay at a sight or camp ground that only has 30 amp service.
Never is a really restrictive word. We always get a 50 amp site when available. But there are some really scenic places we have stayed and have used 30 amp where 50 was not available. And we have often stayed in the mountains at >8,000' in July/Aug when the lows were in the 40's and highs in the 70's and A/C was never turned on. 50 amp was not needed.


And using a 50/30 adapter, it splits the 30 amp current thru the two hot legs making the current thru each leg much less than possible with full 50 amp service.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 10-04-2019, 09:23 AM   #17
DmaxDually
Montana Fan
 
Join Date: Mar 2014
Location: New Port Richey
Posts: 438
M.O.C. #14092
Quote:
Originally Posted by BB_TX View Post
Never is a really restrictive word. We always get a 50 amp site when available. But there are some really scenic places we have stayed and have used 30 amp where 50 was not available. And we have often stayed in the mountains at >8,000' in July/Aug when the lows were in the 40's and highs in the 70's and A/C was never turned on. 50 amp was not needed.


And using a 50/30 adapter, it splits the 30 amp current thru the two hot legs making the current thru each leg much less than possible with full 50 amp service.
I understand..Never was the wrong word to use. Right now now I am not retired and my camping is just quick get aways for rest and relaxation. My camping radius is limited to about 100 Mile weekend and extended weekend trips. So I have the ability to choose local camp grounds that have 50 amp service and all the amenities that I want so I can enjoy the weekend. When I retire and my camping is for sight seeing and exploring the country then I'll take what available..
__________________
2012 Silverado 3500HD|4x4|Crew Cab|long bed|Dually
2012 Montana 3750FL
DmaxDually is offline   Reply With Quote
Old 10-04-2019, 10:38 AM   #18
Carl n Susan
Site Team
 
Carl n Susan's Avatar
 
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,356
M.O.C. #4831
Quote:
Originally Posted by margerush View Post
richfaa--I want a 90 degree dog bone but can't find one. I bought & returned one from etrailer. The 90 hung to the side (not down) & needed to be twisted to the right, therefore, the weight of my power cord pulled it down & made a bad connection. Please suggest who I can get a good 90 degree perpendicular to the ground.
The standard for a 50 male receptacle is to have the ground plate at 8 o'clock. Most every Montana I have ever seen have it 120 degrees off. It is a simple task to remove the housing, the three screws holding the socket, give the socket a twist and them re-install the screws and housing.

This also gives you an opportunity to ensure the lugs holding the 50 amp cable are *TIGHT*. There have been numerous posts recently of folks who have melted the receptacle and power cord together due to loose connections.
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB

Carl n Susan is offline   Reply With Quote
Old 10-04-2019, 01:57 PM   #19
PeteandJoan
Montana Fan
 
Join Date: Oct 2015
Location: Round Rock
Posts: 475
M.O.C. #17905
Quote:
Originally Posted by margerush View Post
richfaa--I want a 90 degree dog bone but can't find one. I bought & returned one from etrailer. The 90 hung to the side (not down) & needed to be twisted to the right, therefore, the weight of my power cord pulled it down & made a bad connection. Please suggest who I can get a good 90 degree perpendicular to the ground.
After you get your dog bone AND after you reposition your electrical inlet plug on the back of the rig so that the bone hangs "mostly" straight down.....then you need to get the coupling kit to seal the connection from your cord to the bone.
https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1. Not sure I did this link properly.

try the link above. I just purchased this about 2 months ago on Amazon (Marinco product) and it works great. It will keep the connection sealed and also hold the cord in place so it does not try to disconnect from dog bone. I leave my dog bone attached to the cord when storing to travel and it stays tight.
__________________
Pete & Joan & "Honey" fur-baby.
2015 Montana 3611RL 2012 F350 6.7 DRW Lariat
Disc Brakes & Sailun 14 ply S637
6-pt Hydraulic leveling
PeteandJoan is offline   Reply With Quote
Old 10-04-2019, 06:38 PM   #20
jcurtis934
Montana Master
 
Join Date: Sep 2013
Location: Pensacola (mail forward service)
Posts: 3,198
M.O.C. #13740
I won't stay at a park with only 30 amp service. I have in the past and had brownouts, but NOT from my power use but others in those parks and/or bad park power. It was hard to tell at one park because initial power was only 116vac. And now we fulltime and have no need to stay at 30 amp site rv parks.
__________________
2012 F350 6.7 L dually, 2013 3800RE with 6 pt leveling, Sumitomo 17.5" load range h tires, Samsung 18 cu ft residential fridge, 8k Morryde I.S. with disc brakes. Full timing since 2012.
jcurtis934 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:25 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.