For the HVAC guys

My A/C trips the breaker for time to time during the hot part of the day. It seems to happen after it has run a long time and can't keep up with rising heat. Even with my second A/C unit, temperatures get up to 84 when it is 100+ outside. Is the main unit about to have trouble or do I already have trouble?
 
stiles watson is offline   Reply With Quote
Old 06-18-2011, 05:26 PM   #2
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,160
M.O.C. #6433
Looking forward to the answers.
We arrived at Palo Duro Canyon State Park on Thursday. Temp was about 104. Turned on both ACs. Rear tripped the 20 amp breaker after about 15 minutes. Reset it and it would only run 2-3 minutes before tripping again. Would wait 10-15 minutes and try again. Would trip after 2-3 minutes. This continued until about sundown when the outside temp started cooling down. Then it ran fine all night.
Next day it was very hot again, but it only tripped one time.
Today in Raton, much cooler (mid 80's) and it never tripped.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-18-2011, 05:38 PM   #3
scductman
Montana Master
 
Join Date: Jun 2007
Location: Eastern
Posts: 1,155
M.O.C. #7270
Stiles mine did that when it was only about 1 yr old. if the breaker has tripped several times it will not hold as much amps. I changed mine for a new one and never had another problem. JMHO
Bobby
scductman is offline   Reply With Quote
Old 06-19-2011, 01:49 AM   #4
ole dude
Montana Master
 
Join Date: Apr 2007
Location:
Posts: 992
M.O.C. #7128
If'n you have an amp meter and if you know the rated load amps of your a/c unit,and have the proper voltage, you could know by measuring the amps if the unit is over amping. Providing that the power supply is sufficient and you are not over amping, then it is doubtful of unit problems. Bobbie's tip, may be the solution. Many times the agency that rates these units does so based on 95 deg outdoor temp and 75 deg indoor temp. When you fall out of those parameters, things can go awry. When the temps get into the range of over 100 deg and are out of design parameters the head pressure gets up there real high causing the compressor to work much harder to pump against the higher pressure and the unit will pull ampheres beyond rated amps causing the breaker to do its job and trip. No solution, just information. Although not practical and in many places forbidden, a water sprinkler on the roof would do wonders, just sayin.
ole dude is offline   Reply With Quote
Old 06-19-2011, 02:23 AM   #5
HOOK
Montana Master
 
Join Date: May 2011
Location: Fayetteville
Posts: 4,200
M.O.C. #11401
Circuit breakers are not expensive. Replace it just for peace of mind. If problem continues take further steps.
HOOK is offline   Reply With Quote
Old 06-19-2011, 03:20 AM   #6
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Good advice, breaker tripping on A/C units can be as simple as a bad breaker, but usually it is loose wiring at the breaker connection, possibly downstream at the unit itself.
High head pressure tripping closely matches the symptoms you describe, Cottonwood seeds in the air where you are? The single most occurring culprit. Check the coil on the roof, see if it looks obstructed. These units are designed to run in very hot weather and stay on, but all conditions have to be right. I think your unit is fine, as it runs for some time when loaded up.
Ozz is offline   Reply With Quote
Old 06-19-2011, 04:11 AM   #7
stiles watson
Montana Master
 
Join Date: Sep 2004
Location: Leona
Posts: 6,382
M.O.C. #2059
Note to self: Clean coils on roof and change out breaker.
stiles watson is offline   Reply With Quote
Old 06-19-2011, 10:04 AM   #8
Bill-N-Donna
Montana Master
 
Bill-N-Donna's Avatar
 
Join Date: Apr 2007
Location: South Shore
Posts: 6,009
M.O.C. #7110


I just went through the same thing recently. I had the coils cleaned really well. It seemed to run better but I had to get the HVAC guy back over to look at it and his recommendation was to replace the unit. I suspect that ours was used on a full time bases before we got it. I use it a lot even when we’re not camping so I think 10 years was good service from it. The new one is doing much better!

__________________
2011 GMC 4X4 dually CC, 6.6 Duramax with Allison Transmission. Formally 2001 Montana,2007 3400RL Montana, presently 2018 3401RS Alpine.
Bill-N-Donna is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
HVAC Dam Worker Montana Problems, Problem Solving & Technical Help 9 05-29-2015 10:52 AM
A few HVAC ones Ozz Sitting around the Campfire 2 04-08-2013 12:46 PM
HVAC work Ozz Sitting around the Campfire 5 11-04-2010 04:34 AM
The new guys... Montana_4069 New Member Introductions 15 07-29-2005 08:21 AM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:01 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.