AC slightly cool but not cold

I have an 8 year old 3150. We had the bedroom AC replaced around year 3 when it was under warranty. This past weekend we noticed that the bedroom AC was running slightly cool but certainly not cold. The living room AC was pumping out cold air and that is what saved us. The BR AC did just enough to keep air circulating but the cold air was coming from the living room.

When I got home I pulled off the cover of both and was prepared to clean the condenser. Both looked like they had just been washed but I cleaned them anyway.

Maybe it's just my bad luck but to have two bedroom, roof top ACs go out in 8 years but that seems like a long shot. Most everything I have read says that when the AC quits blowing cold most of the time you have to replace them since there is no Freon to refill and you would never replace just the compressor.

I know, I need to take it to a service shop and no, I am not a handyman.

The only reason I am posting this is just in case there is someone who has the same thing happen and there is some reasonably simple answer that I can try.
 
Ejenkins is offline   Reply With Quote
Old 05-30-2018, 10:39 AM   #2
kdeiss
Montana Master
 
Join Date: Feb 2003
Location: Englewood
Posts: 3,095
M.O.C. #164
Ejenkins, The temperature of the Air coming out of the AC unit should be 18 to 20 degrees cooler then the inbound you measure the temp at the unit by the filter open the louvers on the outbound air. If you are not getting those readings something is wrong. Dometic had some defective evaporator coils mine was a 2013 model BriskAir ii
The Main unit was replaced twice and the Bedroom once. Dometic is silent recall they will replace the unit not labor. You need the serial numbers and models. If you are interested I believe I have an Email address.
kdeiss is offline   Reply With Quote
Old 05-30-2018, 10:44 AM   #3
kdeiss
Montana Master
 
Join Date: Feb 2003
Location: Englewood
Posts: 3,095
M.O.C. #164
techservice@dometicusa.com


Tech Service 800 216 5115
kdeiss is offline   Reply With Quote
Old 05-30-2018, 10:47 AM   #4
jeffba
Montana Master
 
Join Date: Oct 2017
Location: Bastrop
Posts: 2,892
M.O.C. #20753
LOL another good use for my thermopop.
__________________
Mocha, one-eyed toothless, hurricane survivor, Pirate dog
2019 20th Anniversary Edition 3701LK
B&W 20K for Ford OEM Puck
2018 Ford F-350 Lariat CCLB PSD DRW KJ5CQH
jeffba is offline   Reply With Quote
Old 05-30-2018, 10:52 AM   #5
kdeiss
Montana Master
 
Join Date: Feb 2003
Location: Englewood
Posts: 3,095
M.O.C. #164
Here are the date range for Dometic Briskair ii For Defective Evaporator Coil


time period including all of 2013, 2014 and Jan Feb Mar 2015.
kdeiss is offline   Reply With Quote
Old 05-30-2018, 02:08 PM   #6
Ejenkins
Established Member
 
Join Date: Oct 2009
Location: Shreveport
Posts: 20
M.O.C. #9799
Quote:
Originally Posted by kdeiss View Post
Ejenkins, The temperature of the Air coming out of the AC unit should be 18 to 20 degrees cooler then the inbound you measure the temp at the unit by the filter open the louvers on the outbound air. If you are not getting those readings something is wrong. Dometic had some defective evaporator coils mine was a 2013 model BriskAir ii
The Main unit was replaced twice and the Bedroom once. Dometic is silent recall they will replace the unit not labor. You need the serial numbers and models. If you are interested I believe I have an Email address.


Kdeiss, I am very interested in the email address. Thank you for providing.
Ejenkins is offline   Reply With Quote
Old 05-30-2018, 02:19 PM   #7
kdeiss
Montana Master
 
Join Date: Feb 2003
Location: Englewood
Posts: 3,095
M.O.C. #164
Ejenkins, Take off the Filter Grill with a flash light look up and you will see the name plate if you can not read you can peal off just take care. Email Dometic with Model and Serial and ask if you unit is part of the recall
kdeiss is offline   Reply With Quote
Old 06-01-2018, 08:56 AM   #8
Ejenkins
Established Member
 
Join Date: Oct 2009
Location: Shreveport
Posts: 20
M.O.C. #9799
I was fortunate on this one. The AC was replaced in 9/2016 with a 2 year warranty.
Ejenkins is offline   Reply With Quote
Old 06-01-2018, 09:06 AM   #9
mhs4771
Montana Master
 
mhs4771's Avatar
 
Join Date: Dec 2009
Location: Sebring
Posts: 3,658
M.O.C. #9969
We have Friends who have had there AC replaced Five (5) times on a three year old Grand Design.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
mhs4771 is offline   Reply With Quote
Old 06-01-2018, 09:43 AM   #10
rtolbert2
New Member
 
Join Date: Sep 2017
Location: Lumberton
Posts: 4
M.O.C. #20544
I have a 2018 Montana with Dometic a/c. The bedroom unit changes from Fahrenheit to celcius by touching/bumping the wall. I have set the unit to auto and mid sixties for nights, but after a few hours the blower goes off but the room remains cool. Does anyone have any suggestions?
rtolbert2 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 06:48 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.