I recall someone having a Hughes 50 amp Autoformer for sale sometime back but I can't find it now. Does anyone remember this????

I am parked next to an "Electrician" and he claims that the autoformer takes power from the rest of the park to boost the power it provides. He says you can't produce power you don't have. I have read how this thing works and feel he is wrong, but, being electrically challenged (nice way to say ignorant), I don't know that you can raise voltage by reducing amperage as it says on their website.

Would anyone like to chime in on this?? Would appreciate a real electricians point of view......

Thanks in advance....

Phil
 
exav8tr is offline   Reply With Quote
Old 08-16-2008, 11:42 AM   #2
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
He is not a electrician and he is wrong... I had one for sale and sold it to a fellow MOC'er.. They are a good investment if you have the need.
richfaa is offline   Reply With Quote
Old 08-16-2008, 11:51 AM   #3
exav8tr
Montana Master
 
Join Date: Sep 2006
Location: Casa Grande
Posts: 5,369
M.O.C. #6333
That's what I thought Rich, like being a backroom lawyer eh? I've heard of park owners not allowing them for the same misguided thought.....How does the autoformer tie in with the EMS system. I imagine the EMS would be plugged into the autoformer and the Montana plugged into the EMS with the autoformer plugged into the CG. Am I right in my thinking???
exav8tr is offline   Reply With Quote
Old 08-16-2008, 11:55 AM   #4
awaywego
Montana Master
 
Join Date: Nov 2002
Location: Midlothian
Posts: 956
M.O.C. #40
Phil
He may be 3% right but 97% wrong. An autoformer is nothing but a stepup transformer and yes it may pull 2 or 3 volts more but it boost it 10%. It uses inductance. check this out http://www.allaboutcircuits.com/vol_2/chpt_9/2.html
Good luck but you will not win.
awaywego is offline   Reply With Quote
Old 08-16-2008, 11:56 AM   #5
SlickWillie
Montana Master
 
Join Date: Dec 2006
Location:
Posts: 2,376
M.O.C. #6575
Print this for him to read. It is basically a variable transformer.
SlickWillie is offline   Reply With Quote
Old 08-16-2008, 12:21 PM   #6
ols1932
Montana Master
 
Join Date: Aug 2004
Location: Cedar Rapids
Posts: 4,876
M.O.C. #1944
exav8tr,
That guy is completely wrong. It does not draw down on the park's power. As a matter of fact, it probably helps because the autoformer does not load down the power. It merely steps it up for your use. Every once in a while you will run into a park where the manager has a closed mind about autoformers. Sometime in their past years someone "told" them that autoformers load down the park's power system. Nothing could be further from the truth.

I've used autoformers for years when needed.

Orv
ols1932 is offline   Reply With Quote
Old 08-16-2008, 12:34 PM   #7
exav8tr
Montana Master
 
Join Date: Sep 2006
Location: Casa Grande
Posts: 5,369
M.O.C. #6333
Will, Thanks, that's where I got my info. My concern is it is from Hughes!!!

Wayne, Thanks for the crash course on transformers. What caught my eye is that you cannot produce power you don't have. But what I read from Hughes is they are converting Amps to Volts to boost the power. My dilemna is: If CG power drops below 116 volts and the autoformer boosts that up, how can you get more power from the CG if it is low to begin with? I wish I had more knowledge of electricity..

Orv, Thanks for your input also....
exav8tr is offline   Reply With Quote
Old 08-16-2008, 01:03 PM   #8
ols1932
Montana Master
 
Join Date: Aug 2004
Location: Cedar Rapids
Posts: 4,876
M.O.C. #1944
I have the Hughes and I believe that it won't boost the voltage above 130 volts. It has a cutoff, if I remember correctly. If you have 116 volts, you don't need to boost it.

Orv
ols1932 is offline   Reply With Quote
Old 08-16-2008, 01:40 PM   #9
stiles watson
Montana Master
 
Join Date: Sep 2004
Location: Leona
Posts: 6,382
M.O.C. #2059
I attended a seminar at Escapees Escapade in June where the subject was electrical boost and protection systems. Neither of the instructors were Hughes connected. This question came up and both of them stated definitely that the Autoformer or any such device does not steal power for the campground source. Both touted themselves to be electrical engineers and system designers.
stiles watson is offline   Reply With Quote
Old 08-16-2008, 01:47 PM   #10
noneck
Montana Master
 
Join Date: Sep 2006
Location: Wappingers Falls
Posts: 1,303
M.O.C. #6263
Send a message via AIM to noneck
It is a balance system, if voltage is low it draws more current to keep its output voltage constant. You can't draw more than the power post will allow...which is an ampere limit terminated by the circuit breaker size. So...what it all means is YOU will find in low voltage parks you can't run the same number of devices as the circuit breaker will trip, the park will not suffer from you gaining extra from them.
Chuck
noneck is offline   Reply With Quote
Old 08-16-2008, 02:28 PM   #11
exav8tr
Montana Master
 
Join Date: Sep 2006
Location: Casa Grande
Posts: 5,369
M.O.C. #6333
Well, There you go....Thanks to everyone for your input. Now, Anyone gotta autoformer for sale????
exav8tr is offline   Reply With Quote
Old 08-17-2008, 06:22 AM   #12
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
Google step up transformers then ask the "electrician" if he ever heard on one..it is electronics 101. Everything that we use pulls amps and volts from the campground power as it does anywhere.When we all turn on our A/C's and the C.G power goes down down does that mean we are stealing power??? The "electrician" flunked basic electricity.
richfaa is offline   Reply With Quote
Old 08-18-2008, 03:56 AM   #13
bncinwv
Montana Master
 
Join Date: Feb 2007
Location: Winfield
Posts: 7,327
M.O.C. #6846
Most things electrical has to comply with what is a really simple law. Simply put wattage equals amperage times voltage. Any difference in voltage (autoformer boost) will therefore result in a decrease in amperage (the sum will always equal what is assumed to be a constant wattage). So if our voltage boost is for instance equivalent to 10 volts, then the corresponding amperage decrease is approximately 4 amps. So you will have the proper voltage to prevent electrical harm to sensitive equipment but will have reduced amperage which affects the number of simultaneous draws you can have on the system. It is a little more complicated but this at least provides you with a basic understanding of how the autoformer works, it does not draw any more noticeable power from the campground grid. The cheapest transformer price I found when purchasing was from Tweetys.com.
Bingo
__________________

Bingo and Cathy - Our adventures begin in the hills of WV. We are blessed by our 2014 3850FL Big Sky (previous 2011 3750FL and 2007 3400RL) that we pull with a 2007 Chevy Silverado Classic DRW CC dually.
bncinwv is offline   Reply With Quote
Old 08-18-2008, 02:13 PM   #14
exav8tr
Montana Master
 
Join Date: Sep 2006
Location: Casa Grande
Posts: 5,369
M.O.C. #6333
Bingo,Are you aware the autoformer is boosting when it is boosting? I think I understand the relationship between boosting volts and losing amps, but if the autoformer is boosting the power and you exceed the amp rating I would assume you would blow a breaker. In order to keep from doing this, is there a way of knowing when you are on reduced amps???
exav8tr is offline   Reply With Quote
Old 08-18-2008, 03:09 PM   #15
ols1932
Montana Master
 
Join Date: Aug 2004
Location: Cedar Rapids
Posts: 4,876
M.O.C. #1944
exav8tr,
I know you asked Bingo the question but I want to add my own thoughts. The autoformer will not "over boost" if that's what you're concerned about. I have had my autoformer connected when voltage input was 99 volts and the autoformer boosted it to 110 volts (as read on my internal meter in the rig). I've left the autoformer connected when the input to it was 120 volts and it didn't boost any measurable amount (again as read on my meter inside the rig).

Orv
ols1932 is offline   Reply With Quote
Old 08-18-2008, 04:21 PM   #16
bsmeaton
Montana Master
 
Join Date: Aug 2006
Location: Lone Tree
Posts: 5,615
M.O.C. #6109
Hate to throw a wrench here - but you certainly can pull more than your share of power off the pedestal (nothing to do with Autoformer).

Don't be confused by the rating of the breaker. The rating on that breaker only means that breaker is designed to trip open if that amperage is exceeded, however the mechanism for tripping that breaker is thermal energy or plain old heat on the conductor. By bringing up power consumption slowly without spikes such as motor starts, etc., you can consume far more amperage than the breaker is rated at, with most of the heat being absorbed in your power cord.

I'm sure we all have stories of using our older 30A service and we got away with running the AC, microwave, and watched TV. Those three appliances themselves combined with the converter are actually sneaking closer to 40A through that 30A breaker. Every once in a while the breaker trips, we reset it, but if we ever grabbed that 20' yellow cord on the ground we would quickly learn where the heat is being absorbed. If you've ever hung Christmas lights and noticed that after 10 extension cords and 25 sets of lights your power cord is melting its way through the snow bank, you are probably way overloading that 15A or 20A breaker and getting away with it because the heat is being dispersed before it gets to the breaker.

blah-blah-blah Anyway - can you steal more than your fair share at the pedestal? - certainly - and most big rigs probably do routinely without them even knowing it, which causes the park surges and voltage drops. Is the autoformer a mechanism for you to steal extra power? no- in fact, it is helping you overcome the surges caused by the overloading of other campers.

bsmeaton is offline   Reply With Quote
Old 08-19-2008, 02:38 AM   #17
bncinwv
Montana Master
 
Join Date: Feb 2007
Location: Winfield
Posts: 7,327
M.O.C. #6846
Whew!! What Brad said!!, but to answer your question Phil, remember my Autoformer is in my battery bay so I have no means to monitor it. There is an indicator light on the unit (that is how I knew I was boosting the voltage when I was at Myrtle a couple of times). I have yet to trip a breaker because of reduced amperage when using the Autoformer (which may be related to what Brad said above). Breaker trips are usually related to the same things anyway (namely electric heaters, hair dryers and coffee pots being on a circuit which won't handle simultaneous loads). And no matter what, I have to endure those occasional breaker trips because it does no good to try to get the women to add up the amperage of what they are using and knowing what the breaker rating is. I did teach them that when something does trip, to reset the breaker. I felt that was as good as it was going to get. I firmly believe in the Autoformer and will not do without one in the future (as well as the EMS and surge protection system). One thing to consider is that the Autoformer installation can be such that it is the sacrificial lamb with regards to surges, but the Hughes has a two year warranty and from what I understand they will replace the MOV's under this warranty regardless of the failure cause. I think this would strongly warrant the purchase of a new unit rather than a used one. Food for thought and I hope that we all have been of some help.
Bingo
bncinwv is offline   Reply With Quote
Old 08-19-2008, 03:27 AM   #18
exav8tr
Montana Master
 
Join Date: Sep 2006
Location: Casa Grande
Posts: 5,369
M.O.C. #6333
Thanks everyone for responding, most helpful.

Orv, Not concerned about "overboosting" rather the diminished amps available while boosting. If the autoformer "gives up amps to boost voltage", my concern was the reduction in amps available to "power things". I think Brad answered this question sufficiently, (thanks Brad). You did mention you can monitor voltage inside rig, what device do you use to do this??

Bingo, Thanks for your input also. When on 30 amp service at a park, we have to put a sticky on the microwave that says turn off AC before using. Your point is well taken about a "new" unit versus a used one.

Rich, I already figured the "electrician" I spoke with might not have had all his wires arcing properly.....
exav8tr is offline   Reply With Quote
Old 08-19-2008, 04:13 AM   #19
SlickWillie
Montana Master
 
Join Date: Dec 2006
Location:
Posts: 2,376
M.O.C. #6575
Quote:
quote:Originally posted by bsmeaton

Hate to throw a wrench here - but you certainly can pull more than your share of power off the pedestal (nothing to do with Autoformer).

Don't be confused by the rating of the breaker. The rating on that breaker only means that breaker is designed to trip open if that amperage is exceeded, however the mechanism for tripping that breaker is thermal energy or plain old heat on the conductor. By bringing up power consumption slowly without spikes such as motor starts, etc., you can consume far more amperage than the breaker is rated at, with most of the heat being absorbed in your power cord.

I'm sure we all have stories of using our older 30A service and we got away with running the AC, microwave, and watched TV. Those three appliances themselves combined with the converter are actually sneaking closer to 40A through that 30A breaker. Every once in a while the breaker trips, we reset it, but if we ever grabbed that 20' yellow cord on the ground we would quickly learn where the heat is being absorbed. If you've ever hung Christmas lights and noticed that after 10 extension cords and 25 sets of lights your power cord is melting its way through the snow bank, you are probably way overloading that 15A or 20A breaker and getting away with it because the heat is being dispersed before it gets to the breaker.

blah-blah-blah Anyway - can you steal more than your fair share at the pedestal? - certainly - and most big rigs probably do routinely without them even knowing it, which causes the park surges and voltage drops. Is the autoformer a mechanism for you to steal extra power? no- in fact, it is helping you overcome the surges caused by the overloading of other campers.

Hmmm, I just can't agree with all of that. If you put a constant overload on a breaker, the breaker will heat up internally, regardless of how much heat you dissipate downstream. JMHO
SlickWillie is offline   Reply With Quote
Old 08-19-2008, 06:01 AM   #20
bsmeaton
Montana Master
 
Join Date: Aug 2006
Location: Lone Tree
Posts: 5,615
M.O.C. #6109
Quote:
quote:Originally posted by SlickWillie

Hmmm, I just can't agree with all of that. If you put a constant overload on a breaker, the breaker will heat up internally, regardless of how much heat you dissipate downstream. JMHO
It's all about heat Slick, the breaker actually cannot detect amperage. With enought heat sinks downstream, you can practically double the amperage passing through that breaker. The most common examples of overloading are commercial office areas. I've seen the male end of a multi-outlet strip melt through the outlet on the wall and drip down onto the carpet while continously serving 3 office cubes, each running a 1500Watt space heater, computers, and flourescent lights. The breaker, located 300 feet away in the electrical room, was only 20A. It never tripped, nor was it even warm. Our clamp-on Amp meter indicated a 48A draw on that multioutlet strip.
bsmeaton is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Autoformer Jdrobone Additions & Improvements 11 02-17-2010 02:59 PM
30 amp autoformer chas Trailers, Tow Vehicles & RV related items for Sale 3 10-11-2008 05:10 PM
Autoformer richfaa Additions & Improvements 10 05-12-2006 02:51 AM
Autoformer harleyrider Additions & Improvements 33 02-24-2006 11:20 AM
Autoformer ???????? Dano General Discussions about our Montanas 3 01-14-2006 05:22 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 06:52 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.