what won't run on 30 amp?
A question for you more experienced campers:
So far our camping has all been in warmer temperatures so we always made sure that we had 50 amp service to run both A/C's. We are considering a fall/winter trip not too far from home and some of the parks we are considering have full hookups except that the electrical is only 30 amp. I know that both A/C's need 50 amp to run, but except for that, what will or will not run simultaneously while on only 30 amp service? TIA.
|
|
|
11-20-2017, 11:14 AM
|
#2
|
Montana Master
Join Date: Jun 2017
Location: POINTBLANK
Posts: 1,888
M.O.C. #19944
|
I'll be interested in that answer - thanks for asking
__________________
RAM 22' DRW 3500 Crew LB 40 gal reserve tank / RETRAX Bed Cover / 2020 373RD HC / IS / MOPEKA Tank Monitor / Furrion Side&Rear Cameras
Slide Toppers / EMS-HW50C / Sailun 85's
3rd AC / Dometic 320
|
|
|
11-20-2017, 11:44 AM
|
#3
|
Montana Fan
Join Date: Aug 2012
Location: Fowler
Posts: 414
M.O.C. #12748
|
You can run everything but the two AC units. BUT caution must be taken to ensure that only ONE heavy usage item, microwave, hair dryer, electric heater, etc. is on at any given time or you will pop the breaker. It won't take you long to learn how to control your usage once you make several trips to the pedestal to reset the breaker.
|
|
|
11-20-2017, 01:13 PM
|
#4
|
Montana Master
Join Date: Oct 2012
Location: Box Elder
Posts: 4,701
M.O.C. #12947
|
When we are connected to a 30 amp pedestal, I turn the fridge and water heater to gas only. When we are using an air conditioner, we turn it off to use a microwave, or the wife's hair dryer. Like was said, you will learn pretty quick what you can run and can't when only having less than 1/3 of the power available when connected to a 50 amp service.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
|
|
|
11-20-2017, 01:54 PM
|
#5
|
Montana Master
Join Date: Dec 2005
Location: Eugene
Posts: 1,053
M.O.C. #5091
|
Don't use the hair dryer and the fireplace at the same time. The only time I use the 50amp is when we were down in Arizona for the winter staying 3 months.
|
|
|
11-20-2017, 01:57 PM
|
#6
|
Montana Master
Join Date: Oct 2004
Location: Salem
Posts: 7,550
M.O.C. #2283
|
I have a High Country with 50 amp service and never even bother to take the 50 amp cord with us.
Lynwood
|
|
|
11-20-2017, 03:25 PM
|
#7
|
Montana Master
Join Date: Apr 2006
Location: Mesa az
Posts: 2,953
M.O.C. #5651
|
Any heater will use 11-12 Amps. Microwave is about 11-12 also. So usually fine. However, the converter can use 8-10 amp at times. I have a surge protector and noticed that for each 12V light I turn on, the amps go up about 2. So if you turn on 3 or 4 lights things could go 'pop' in the night!!!!! As others said, just use one at a time.
__________________
Tom and Gail
2013 Mountaineer 362
2012 Silverado 2500
|
|
|
11-20-2017, 06:07 PM
|
#8
|
Montana Master
Join Date: Oct 2012
Location: Box Elder
Posts: 4,701
M.O.C. #12947
|
The electric use with conventional light bulbs is a good reason to upgrade to LED bulbs. When we still had regular bulbs, with most of them turned on, the fan in the converter would start almost immediately, and since replacing all of them with LED's, the fan rarely runs. That's a pretty good indication of how much load regular bulbs draw.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
|
|
|
11-20-2017, 07:36 PM
|
#9
|
Site Team
Join Date: Sep 2017
Location: Oro Valley
Posts: 3,932
M.O.C. #20477
|
Running the heat pump draws quite a bit also. You can do pretty much all you need on 30 amps just need to manage your use.
__________________
Zack and Donna plus Millie and Ranger
2018 3160RL
"Life is too short to stay indoors, enjoy the ride!"
|
|
|
11-20-2017, 08:36 PM
|
#10
|
Montana Master
Join Date: Jun 2017
Location: POINTBLANK
Posts: 1,888
M.O.C. #19944
|
Watch LED's - small quantities are ok, large are not. LED have a little published trait called in RUSH CURRENT. Some Controls companies de-rate controls by 50% - kinda of like an A/C - pulls heavy current to start it
__________________
RAM 22' DRW 3500 Crew LB 40 gal reserve tank / RETRAX Bed Cover / 2020 373RD HC / IS / MOPEKA Tank Monitor / Furrion Side&Rear Cameras
Slide Toppers / EMS-HW50C / Sailun 85's
3rd AC / Dometic 320
|
|
|
11-21-2017, 04:58 AM
|
#11
|
Montana Master
Join Date: May 2011
Location: Hixson
Posts: 3,436
M.O.C. #11397
|
Quote:
Originally Posted by Ram Montana High Country
Watch LED's - small quantities are ok, large are not. LED have a little published trait called in RUSH CURRENT. Some Controls companies de-rate controls by 50% - kinda of like an A/C - pulls heavy current to start it
|
Hmmmmmmm? Our new 2018 is all LED.
__________________
2018.5 Montana 3791RD
Full Timers 9/1/2010 through 1/16/2020.
|
|
|
11-21-2017, 05:09 AM
|
#12
|
Montana Master
Join Date: Mar 2017
Location: Winchester
Posts: 900
M.O.C. #19514
|
Our previous trailers were all 30 amp. I had no trouble running the regular stuff like fridge and water heater, etc. The only thing I found was I couldn't use my Dyson canister vacuum while the a/c was running. Now that we have a trailer with 50 amp, wouldn't you know I am no longer bringing the canister vacuum but instead have a smaller (Shark) vacuum for in the trailer. I only brought the Dyson when we wintered in Florida. Since we only have one a/c unit in the Monty, I don't think we will have a problem anywhere we go.
__________________
2017 High Country 305RL
2015 Ford F-250 Super Duty
|
|
|
11-21-2017, 06:53 AM
|
#13
|
Montana Fan
Join Date: Jun 2015
Location: Livermore
Posts: 321
M.O.C. #17521
|
I have a older Montana 03 and never had a problem hooking to 30 amps. I run the air and microwave without any problems so far.
|
|
|
11-21-2017, 08:02 AM
|
#14
|
Site Team
Join Date: Jun 2011
Location: Wilsey
Posts: 18,799
M.O.C. #11455
|
We spent some time one summer with 30amps and were fine unless the AC and the fridge came on with the microwave or another high draw item. Never had trouble with the AC, frig and hot water heater until something else was added to the mix.
|
|
|
11-21-2017, 08:18 AM
|
#15
|
Montana Master
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
|
These Montana's use a lot of power they are 50 amps per leg for a reason . When in Oklahoma last summer with temps of 107 plus we saw 32 amps on leg one and 28 amps on leg 2.
|
|
|
11-21-2017, 10:00 AM
|
#16
|
Montana Master
Join Date: Jun 2017
Location: POINTBLANK
Posts: 1,888
M.O.C. #19944
|
The In-Rush should not be an issue with the standard set quantity of factory installed fixtures. The de-rating would work this way, generally happen to dimmers and motion devices in a circuit. If a dimmer was rated @ 1000 watts incandescent load, the manufacturer would rate the same dimmer for only 500 watts input from lead. Generally, 5ers should be OK, but if a gremlin shows up in some system and there a lot of LEDs - might be a point to investigate. This problem should up after construction start moving to high quantities of LED and big control systems.
__________________
RAM 22' DRW 3500 Crew LB 40 gal reserve tank / RETRAX Bed Cover / 2020 373RD HC / IS / MOPEKA Tank Monitor / Furrion Side&Rear Cameras
Slide Toppers / EMS-HW50C / Sailun 85's
3rd AC / Dometic 320
|
|
|
11-22-2017, 12:16 PM
|
#17
|
Montana Fan
Join Date: Nov 2010
Location: Chatsworth
Posts: 468
M.O.C. #10933
|
At the rally in Goshen, the progressive dynamics rep. Said to remember that there are two 50 amp breakers,one for the left side of the breaker box and one for the right so in effect we have 100 amp. service. I think the same is true for the 30 amp service and thereforer in effect you have 60 amp service, as long as you divide the power usage between the two sides of the service box.
|
|
|
11-22-2017, 05:43 PM
|
#18
|
Montana Master
Join Date: Dec 2009
Location: Sebring
Posts: 3,659
M.O.C. #9969
|
Sorry wrong on the 30 amp service. With the RV 30 amp service there is only one hot leg and only one 30 amp main breaker in the distribution panel, thus 30 amps max.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
|
|
|
11-23-2017, 01:56 PM
|
#19
|
Seasoned Camper
Join Date: Mar 2017
Location: Pine
Posts: 53
M.O.C. #19552
|
Quote:
Originally Posted by Ram Montana High Country
Watch LED's - small quantities are ok, large are not. LED have a little published trait called in RUSH CURRENT. Some Controls companies de-rate controls by 50% - kinda of like an A/C - pulls heavy current to start it
|
Me thinks in-rush current for an LED is for grid powered LEDs, ie 120-240V AC.
In our trailers we don't have 120V LED nor enough to cause a problem with in-rush current.
|
|
|
11-23-2017, 04:38 PM
|
#20
|
Montana Master
Join Date: Dec 2009
Location: Sebring
Posts: 3,659
M.O.C. #9969
|
Changed all the lites in our '10 Montana to LEDs, then all the lites in our SOB, and our current SOB came with all LEDs and never a problem with any of them, other than I never hear the cooling fan in the converter kick on with LED lights on.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
|
|
|
|
|