Quote:
quote:Originally posted by SlickWillie
Quote:
quote:Originally posted by Ozz
John, I haven't tried it, but my dryer would probably work on 30 amps. Depends on the control inside it, but I would bet a box of sugar donuts that it would heat, but on 1/2 power, just take twice as long to dry. I bet the only thing that is 220 is the heating elements, motor is 120 volts, most probably the controls also. I would have to look at the schematic.
|
I don't think it will work on the 30 amp adapter. Both sides of the element will have 120 volts of the same phase which will equal no current flow.
The GFCO 50 amp panel we have is not set up for 240 volts. The only two pole single throw breaker is the one in the middle, which serves as the main. The left and right buss are different phases. I am told the Iota panels are different.
|
You are right Slickwillie, it will not work, it is like having an open leg of a 220 circuit, no current flow equals no heat.