If on a 120/240 volt circuit, there is say 10 amps neutral current from one leg and say 8 amps neutral current from the other leg, you just subtract the difference, and there is only 2 amps current on the neutral. That is the reason the neutral is allowed to be half the size of the hot legs in many circuits. Yes, the current flows in opposite directions in the neutral, but the flows cancel each other out, so the amperage in the neutral is much less than the hot legs.
 
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
rohrmann is offline   Reply With Quote
Old 03-18-2014, 12:52 PM   #22
snfexpress
Montana Master
 
Join Date: Jan 2006
Location: South
Posts: 2,499
M.O.C. #5140
We have stayed at CG's with 100 amp 240 volt service for the larger Class A's that require it. Usually just one or two spots if available.
snfexpress is offline   Reply With Quote
Old 03-18-2014, 03:41 PM   #23
jlb27537
Montana Master
 
Join Date: Jan 2013
Location: Depends on temps
Posts: 1,648
M.O.C. #13157
The advertized 100 A service is just that. 2 50A plugs. Some Prevost type units have 2 50A power cords. Voyager RV Park in Tuscon has several 100A sites as does Skyline RV Ranch in Bandera, Tx.

Stayed at both.

Yes you would need 200A service to feed them. However 30A per leg is usually all is really required.

I did maintenance in both parks.

Jim
__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Old 03-18-2014, 03:43 PM   #24
Phil P
Montana Master
 
Join Date: Mar 2011
Location: Okeechobee
Posts: 2,150
M.O.C. #11206
Quote:
quote:Originally posted by BB_TX

Again I will have to disagree, although it may just be semantics.

You can have 50 amps flowing thru line 1. And at the same time you can have 50 amps flowing thru line 2. So at maximum current flow thru both lines at the same time you can have 12,000 watts of power (100 amps x 120 volts = 12,000 watts).

You can't have more than 50 amps flowing thru either hot leg or any wire at any time. And (at any given time) the current flowing into one leg is flowing out the other leg. So in that respect it is not additive. But you do still get the EFFECT of having a total of 100 amps IF you have loads that would draw the maximum of 50 amps from each hot leg at the same time. The 50 amp breaker is a double pole breaker, each pole rated for 50 amps. Since the hot legs are not additive, you can have up to, but not more than, 50 amps flowing thru each pole and to each separate group of loads simultaneously.
Look at the drawing.

As you pointed out it is AC so one second one end on the transformer is + and the other end is -. The next second that changes. So the current flows thru both breakers at the same time in the same direction.

The power flows between the 2 lines. If you exceed 50 amps anywhere in the circuit you will trip the breaker.

We haven’t been talking wattage at all and if you want to go there then you need also to talk about power factor.

All of the information I have posted came from the text books I just made a typo error. It is a common mistake and I thank you for pointing that out. It is a long course if you study only the AC electrical part 8 hours a day the course takes 2 weeks to finish. It has now been 8 years since I did the last refresher course.

The school I attended for the 2 week course in Tucson had a demonstration panel with amp meters installed in all three lines and as the load was equalized on Line 1 and Line 2 the neutral amperage dropped accordingly until it was no longer readable by the meters being used. The voltage meters wired to neutral remained at 120 volts and the volt meter wired between line 1 and line 2 remained at 240 volts thru the entire demonstration.

The power flows between line 1 and line 2 when the load is equal. The difference between line 1 and line 2 is carried by the neutral.

If this were not the case the neutral wire would have twice the capacity of the wires to line 1 and line 2.

So we play the game with math.

100 amps X 120 volts = 12000 watts

50 amps X 240 volts = 12000 watts

This is simple formula that doesn’t take into account power factor.

Phil P
__________________
2009 Montana 3665RE
2009 Duramax 3500 DRW quad cab
personal web page https://www.sallyscoffees.com
If you get a page not available then remove the "s" after HTTP
Phil P is offline   Reply With Quote
Old 03-18-2014, 04:44 PM   #25
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,155
M.O.C. #6433
As I said, semantics. We have said the same thing in different words and ways. As an electrical engineer and 30 years as a control system design engineer I have been there also.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is online now   Reply With Quote
Old 03-18-2014, 04:46 PM   #26
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,155
M.O.C. #6433
Sorry that this got off the original topic. But good to see that there are some good answers as to the meaning of 100 amp service at an RV park.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is online now   Reply With Quote
Old 03-24-2014, 03:01 AM   #27
ols1932
Montana Master
 
Join Date: Aug 2004
Location: Cedar Rapids
Posts: 4,876
M.O.C. #1944
In reality, when RV parks say they have 50 amp service there are two 50-amp legs on the line providing 100 amps. With the two 50-amp legs they can hook on to one leg for the RV and still have the other 50-amp leg available. This allows them to legitimately say they can provide 100-amps.

Orv
ols1932 is offline   Reply With Quote
Old 03-24-2014, 03:12 AM   #28
K0LCB
Montana Master
 
Join Date: Apr 2013
Location: Arroyo City
Posts: 3,110
M.O.C. #13395
If I remember my basic elect. Theory, and that was a long time ago, I X E = W, applies to a D.C circuit, A.A. Requires you to figure root means squared or something like that.
K0LCB is offline   Reply With Quote
Old 03-24-2014, 04:24 AM   #29
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,155
M.O.C. #6433
Quote:
quote:Originally posted by K0LCB

If I remember my basic elect. Theory, and that was a long time ago, I X E = W, applies to a D.C circuit, A.A. Requires you to figure root means squared or something like that.
Volts times amps equals watts, in a purely resistive circuit. When you get into circuits with inductive loads (such as motors) and capacitive loads then a thing called power factor comes into play. It affects the realized power available from the same voltage.

Root mean square is the method of specifying voltage in an AC circuit. What we know as 120 vac actually has a peak voltage of approximately 169 volts at the high point (and negative 169 at the low point) of the voltage curve. But after doing root mean square calculations it comes out to 120 volts. Since the voltage passes thru zero volts twice each cycle you don't get the full benefit of the 169 volt peaks.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is online now   Reply With Quote
Old 03-24-2014, 04:28 AM   #30
K0LCB
Montana Master
 
Join Date: Apr 2013
Location: Arroyo City
Posts: 3,110
M.O.C. #13395
Thanks Bill! It's been many moons since 1964
K0LCB is offline   Reply With Quote
Old 03-24-2014, 05:02 AM   #31
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
BB TEx,, I remember that but I forgot it 10 mins after I retired. I was however a electronic technician not a electrician and there is a big difference. Folks always thought I could do electrical work and I would say no if you have radar that needs repaired I am your guy otherwise call a electrician.
richfaa is offline   Reply With Quote
Old 03-24-2014, 06:18 AM   #32
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,155
M.O.C. #6433
Yeah, I still have nightmares about it sometimes from my school days oh so many years ago. Even the description above is highly simplified.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is online now   Reply With Quote
Old 03-24-2014, 01:15 PM   #33
catskiner
Montana Fan
 
Join Date: Apr 2009
Location: big pine
Posts: 128
M.O.C. #9253
Some of the newer class A MH are all electric,no propane at all.
catskiner is offline   Reply With Quote
Old 03-24-2014, 03:27 PM   #34
Phil P
Montana Master
 
Join Date: Mar 2011
Location: Okeechobee
Posts: 2,150
M.O.C. #11206
Quote:
quote:Originally posted by catskiner

Some of the newer class A MH are all electric,no propane at all.
The last RV show we went to some of the bigger 5th wheels were equipped with AC refrigerators and 4 large batteries to power an inverter.

The excuse used was a high failure rate for the larger gas refrigerators.

Phil P
__________________
2009 Montana 3665RE
2009 Duramax 3500 DRW quad cab
personal web page https://www.sallyscoffees.com
If you get a page not available then remove the "s" after HTTP
Phil P is offline   Reply With Quote
Old 07-02-2014, 09:13 PM   #35
Papafish
Established Member
 
Join Date: Sep 2013
Location: Boise
Posts: 40
M.O.C. #13739
Hi all. Ok, just to double check so I don't zap my Monty with 220v, if I want a 50 amp 120 volt shore receptical I would use a 220 v double wide breaker and wire one leg to line 1, one leg to line 2, neutral and ground. Correct? Thanks for the help, Steve
Also, why when I make a post does it show up twice?
Papafish is offline   Reply With Quote
Old 07-02-2014, 09:14 PM   #36
Papafish
Established Member
 
Join Date: Sep 2013
Location: Boise
Posts: 40
M.O.C. #13739
Hi all. Ok, just to double check so I don't zap my Monty with 220v, if I want a 50 amp 120 volt shore receptical I would use a 220 v double wide breaker and wire one leg to line 1, one leg to line 2, neutral and ground. Correct? Thanks for the help, Steve
Also, why when I make a post does it show up twice?
Papafish is offline   Reply With Quote
Old 07-03-2014, 01:22 AM   #37
Phil P
Montana Master
 
Join Date: Mar 2011
Location: Okeechobee
Posts: 2,150
M.O.C. #11206
Hi

I have had the double post happen several times. You have a delete button at the top of your post I just delete the second one.

You have the idea on how to wire the 50 amp service for the Montana if you are coming from the breaker box if you are coming from a different receptacle like a range receptacle (3 wire) one of the wires will have to be run out side of the receptacle I don’t remember if this is the ground or the neutral so be careful.

Phil P
__________________
2009 Montana 3665RE
2009 Duramax 3500 DRW quad cab
personal web page https://www.sallyscoffees.com
If you get a page not available then remove the "s" after HTTP
Phil P is offline   Reply With Quote
Old 07-03-2014, 04:40 AM   #38
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,155
M.O.C. #6433
You have the right idea on the wiring. Same as your house wiring. Here is a good source for wiring information.

Sometimes if things are running slow there is a tendency to click Post New Reply twice thinking the first time did not take. The result will be double posts. As Phil stated, just click on the delete button for the second one.

Also since your question was not really directly related to the original question in this discussion, I would suggest you start a new post next time you have a new question to get better results.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is online now   Reply With Quote
Old 07-03-2014, 01:49 PM   #39
jlb27537
Montana Master
 
Join Date: Jan 2013
Location: Depends on temps
Posts: 1,648
M.O.C. #13157
100A service in a RV park means there is 2 50A plugs in the box.

That would be a 50A plug which we all know is 50A on 2 legs of 240ac.

Your larger stuff like Prevost, which are total electric, have 2 50A power cords.

We worked one winter in Tuscon (Voyager) that had a section that they used for the Jewels, 1M priced rigs, and the park we go to in Bandera, Tx has some 100A sites. (Skyline Ranch)

Jim
__________________

2012 Ram Laramie 3500 DRW 4x4 3.73 Tow Max Pkg B&W Companion 60 gal RDS aux fuel tank. 2014 Montana 3150RL, 2 A/C's, Leather, 6 Point Jacks, Splendede WD2100XC, Mor/ryde X-Factor, Duravis 250 tires with TST 507RV monitors. 2 x Honda EU2000's
jlb27537 is offline   Reply With Quote
Old 07-06-2014, 01:15 PM   #40
paulinbaja
Montana Fan
 
Join Date: Feb 2014
Location: Chico
Posts: 269
M.O.C. #14041
We certainly beat the theory to death! It was fun reading the different way people attempt to explain the same thing. One comment that was wrong along the way indicated the neutral can be 1/2 the size of the power legs. This is incorrect, it is the same size in a typical panel wiring. It does not have to be double the size due to the sign wave reversing the polarity! All that has to do with resistive loads, now with 3 phase digital power supplies all that gets adjusted due to the nature of digital power supplies and the way manage power! It is lots of fun!
paulinbaja is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
He said it was a 30-amp service Phil P General Discussions about our Montanas 2 09-01-2011 07:55 AM
50A to 30A service maximo General Discussions about our Montanas 12 05-26-2011 07:50 PM
50 AMP SERVICE Sweetfire Montana Problems, Problem Solving & Technical Help 4 05-03-2006 04:03 AM
Replace 30 A service with 50 A service fulltimedreamer Additions & Improvements 9 01-13-2005 05:46 PM
50 AMP service Montana_186 General Discussions about our Montanas 0 02-27-2003 09:33 AM