Red propane regulator...Update
We had a long discussion here not to long ago about that Red regulator. Ours gave a annoying hummm when drawing from that side. After talks with Ed Lee,sr a Engineer at Marshal controls it was determined that the OEM regulator was not the regulator the system was designed for and suggested we get a new and proper one.... We did and after the customary procrastination period installed it yesterday..
Marshall, on the phone and in the manual said not to use that Thread tape on Gas or propane lines. The instruction sheet that came with the regulator said..do not use thread tape on Gas or Propane lines. I had some thread compound on board..it said..do not use on Gas or propane lines. OK..so I got the message.. went to Home Depot and got some stuff that said.... For use on gas and propane lines...
When I removed the OEM regulatior can you guess what Keystone used on the gas line threads.. Did you guess "tape" that is correct..
Now the syetem never leaked and it was checked as recently as September of this year at the service center
Cost cutting???? or is there tape that you can use on Gas and Propane lines??
|
|
|
12-30-2009, 02:57 AM
|
#2
|
Montana Master
Join Date: Jan 2007
Location: Lobelville
Posts: 2,128
M.O.C. #6650
|
Rich what regulator or type did you replace the OEM system with? Its always amazing what we learn about our 5th wheels. GBY....
|
|
|
12-30-2009, 03:34 AM
|
#3
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,133
M.O.C. #6433
|
They do make a special tape for gas lines.
gas pipe tape
It was originally white, but is now color coded yellow to distinguish it from the basic type.
There are also some other specialty types of tape, also color coded.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
12-30-2009, 04:09 AM
|
#4
|
Montana Master
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
|
Bill OEM tape was white and appeared to be of the same type used on water lines. The red regulator is the one on the doorside or on the "far side" it is 18psi OEM and should be 30psi according to Marshall controls. The correct regulator is part # C6121#2049 30psi From Marshall controls. Cost @40.00 or less..
|
|
|
12-30-2009, 04:16 AM
|
#5
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,133
M.O.C. #6433
|
Gas pipe tape is higher density material to reduce possibility of leaks. But it would not surprise me if they used the basic tape for everything even though they should know better.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
12-30-2009, 04:32 AM
|
#6
|
Montana Master
Join Date: Nov 2003
Location: Santa Fe Springs
Posts: 4,189
M.O.C. #639
|
I use the yellow tape for all my stuff, I dont believe it is harmful to use for water unles I hear differant. it's cost is not the issue for me its less I have to carry in the tool box.
__________________
Pulling a 2004, 2980 RL an oldie but goodie.
Tow vehicle is a 2009 RED RAM 3500 DRW.
|
|
|
12-30-2009, 07:33 AM
|
#7
|
Montana Fan
Join Date: Nov 2007
Location: SW
Posts: 255
M.O.C. #7895
|
I have talked to Ed Lee also. Got my C6121 here: http://rvwholesalers.com/
|
|
|
08-31-2011, 07:00 AM
|
#8
|
Montana Fan
Join Date: Jun 2005
Location: Woodland
Posts: 476
M.O.C. #3890
|
Reviving an old thread.
We've had a propane smell by the curbside tank. I bought a replacement pigtail, only to find that it (and all others I've seen offered) had a 1/4" inverted male flare, while the red 18 PSI regulator accepted a 3/8" inverted male flare. While I've not found the proper pigtail anywhere, I did learn a lot searching the forum. I'm looking for the C 6121 30 PSI regulator now (a search at RV Wholesalers returned no results). In looking, I found this interesting installation instruction from Marshall for the remote side regulator: http://www.shleggitt.com/edlees/5thwheel.html If I'm reading it correctly, pipe thread sealant is applied to the male thread on the regulator, but no sealant is applied to the flare threads on the pigtail.
|
|
|
08-31-2011, 07:46 AM
|
#9
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,133
M.O.C. #6433
|
Bill - You can get one from Makarios RV. That is where I got mine. Seem to be a good company to do business with.
I took the brass fittings out of the new regulator and it matched up to the existing fittings.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
08-31-2011, 03:52 PM
|
#10
|
Montana Master
Join Date: Mar 2010
Location: bloomington
Posts: 540
M.O.C. #10234
|
Gas line tape looks like teflon tape but has a yellow cover on it instead of the blue that teflon tape has. I have used it on several projects and have had no issues.
|
|
|
08-31-2011, 05:16 PM
|
#11
|
Montana Master
Join Date: Feb 2005
Location: Haysville
Posts: 4,261
M.O.C. #3085
|
Pretty much industry wide, pipe tape or pipe dope is used on taper pipe threads as it is necessary for the seal. Putting tape or dope on any flair fitting threads is a waste of effort as the flair surface is what does the sealing ... the threads on the collar just make the connection tight.
|
|
|
09-03-2011, 04:12 PM
|
#12
|
Montana Fan
Join Date: May 2009
Location: Gilbert
Posts: 262
M.O.C. #9307
|
Installed the regulator part # C6121#2049 30psi From Marshall controls on our Montana over a year ago. Replaced the incorrect 18PSI version thst had been made in France or Italy. Had to replace the switchover side regulator as well. In a conversation with Ed Lee from Marshall, Montana was storing the black cross over pipe horizontally in the factory after the ends had been threaded. The threading oil leachedinto the interior of the pipe and when installed in our Montana's, the oil destroyed the two regulators over time. Have not had any problems with either replacement regulator after cleaning the cross over pipe really well and installing the two new regulators. Used a liquid pipe sealer when installing the new regulators. No leaks since.
|
|
|
09-04-2011, 04:23 AM
|
#13
|
Montana Master
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
|
Except for that humming issue we never had a regulator issue. The main regulator is still the OEM one after nearly 6 years. After a conversation with E lee of Marshall a long time ago to we decided to bring the system up to Marshall specs and did order the new red regulator
|
|
|
05-16-2012, 06:07 AM
|
#14
|
Montana Fan
Join Date: Dec 2011
Location: Livingston
Posts: 350
M.O.C. #12009
|
Quote:
quote:Originally posted by Desert RVer
Installed the regulator part # C6121#2049 30psi From Marshall controls on our Montana over a year ago. Replaced the incorrect 18PSI version thst had been made in France or Italy. Had to replace the switchover side regulator as well. In a conversation with Ed Lee from Marshall, Montana was storing the black cross over pipe horizontally in the factory after the ends had been threaded. The threading oil leachedinto the interior of the pipe and when installed in our Montana's, the oil destroyed the two regulators over time. Have not had any problems with either replacement regulator after cleaning the cross over pipe really well and installing the two new regulators. Used a liquid pipe sealer when installing the new regulators. No leaks since.
|
having issues with regulator is this red one set up for dual use and any advice on installation
__________________
2014 3850FL
2008 F350 SRW
David and Liz
|
|
|
05-16-2012, 09:02 AM
|
#15
|
Montana Master
Join Date: Apr 2009
Location: Murrieta
Posts: 5,816
M.O.C. #9257
|
Hey Pugtracker. I saw your other post that had a picture of the changeover regulator.
I have already done this replacement and this is the regulator on the opposite side of the auto switchover regulator.
Now I think I am having a problem with the left side of the auto switchover regulator. Maybe it was caused by the problem someone else described about the thread oil on the pipes, but I'll just replace the auto regulator and hope the problem goes away.
|
|
|
05-16-2012, 03:00 PM
|
#16
|
Montana Master
Join Date: Jun 2010
Location: Colorado Springs
Posts: 3,335
M.O.C. #10496
|
Before you change a regulator, look at the hose that goes from the switchover regulator to the door side regulator. I had this problem and it wound up being a stuck check valve in the hose leading from the switchover regulator to the door side. The repairman just replaced the hose with one that had no check valve and all is good.
__________________
2010 3150RL
LevelUp, Dual 6 volt batteries, Progressive Industries EMS HW50C, Honda EU2000i Generator, Bridgestone Duravis R250 tires, Torklift Glowstep Revolution Stairs, LED Tail lights
2015 RAM 3500 Laramie SRW LB CC Cummins 6.7L Aisin Trans B&W RVK3600
|
|
|
05-17-2012, 02:07 PM
|
#17
|
Montana Fan
Join Date: Jul 2011
Location: madison
Posts: 120
M.O.C. #11617
|
the special hose saves the valve inrush valve from goinccg off all the time and also acts as a safety due to the fact that some times when the change over occurs there will be back leakeage and if not connected to the tank it could conceivably embarrasimg... just something to keep in mind...
I had trouble with the original chicom valves that come in the chicom tanks... I replaced them with usa made tanks and red reg and auto reg... no problem since...
good luck,
|
|
|
05-17-2012, 04:28 PM
|
#18
|
Montana Fan
Join Date: Dec 2011
Location: Livingston
Posts: 350
M.O.C. #12009
|
bougt a new auto change valve as thats all i have, I dontbhave the other pressure valve will install soon and advise all.
__________________
2014 3850FL
2008 F350 SRW
David and Liz
|
|
|
05-18-2012, 11:18 AM
|
#19
|
Montana Master
Join Date: Dec 2010
Location:
Posts: 724
M.O.C. #10948
|
I ordered the Marshall from Makarios as well and they sent me a made in Mexico Precimex and not the Marshall pictured on their website.
|
|
|
05-18-2012, 03:09 PM
|
#20
|
Montana Master
Join Date: Sep 2008
Location: Bangor
Posts: 770
M.O.C. #8816
|
Just an observation, Marshall Ind. says Keystone is using the wrong regulator, should be 30psi. Has anybody barked at Keystone about this? If in fact it's wrong shouldn't Keystone be the one eating the cost. especially if the unit is still under warranty. My propane hums also,c so if it's because of the wrong regulator......... I'll let you all know how I make out.
kevin
|
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
Similar Threads
|
Thread |
Thread Starter |
Forum |
Replies |
Last Post |
Red propane regulator
|
embraceatrend |
Maintenance |
9 |
10-23-2016 07:40 AM |
propane regulator
|
lcarter |
Repairs & Service |
2 |
10-01-2013 01:16 PM |
Propane regulator
|
jrjones |
General Discussions about our Montanas |
5 |
09-30-2013 08:55 AM |
Propane regulator
|
c214dick |
Montana Problems, Problem Solving & Technical Help |
2 |
04-05-2009 07:08 AM |
Propane regulator
|
RLVoumard |
Montana Problems, Problem Solving & Technical Help |
4 |
08-13-2007 05:17 PM |
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|