Old 09-09-2013, 05:17 PM   #1
2BsRetired
Established Member
 
Join Date: Feb 2011
Location: Coquitlam
Posts: 12
M.O.C. #11106
Send a message via Yahoo to 2BsRetired
ac Electrical outlets

I am a retired electrician I was the head electrician for a Hospital in Canada. We have a 2010 Mountaineer and after 3 years almost had a fire in our GFCI outlet at our bathroom sink. When these outlets are put in the factory workers use battery drills to tighten the screws and in our case they were over tightened and stripped. The result was they became loose and over the three years of travelling the white wire burnt off. We have since talked to four other people that have had the same problem. Please check these outlets in your rigs and also put a fire extinguisher at your bed side. If there is a fire in your rig you only have two minutes to put it out or get out. I have also changed all our outlets to standard home outlets as the ones that are in all rigs I believe are inferior. The connections are just a push on not a wire around a screw. The ones that are put in the rigs during manufacturing are up to code however I do not like the type of connection. I have never liked this type of connection even on regular house hold outlets. When I opened the outlet behind our easy chair a wire popped off. AGAIN PLEASE CHECK YOUR GFCI AT MIMIMUM

Bob
 
2BsRetired is offline   Reply With Quote
Old 09-10-2013, 02:14 AM   #2
kdeiss
Montana Master
 
Join Date: Feb 2003
Location: Englewood
Posts: 3,095
M.O.C. #164
I agree a Neighbor here in the Campground with a Montana had no power in one area of the Kitchen, After checking the breakers I started to open up receptacle and I found a pop wire as you described could have easily caused a fire
kdeiss is offline   Reply With Quote
Old 09-10-2013, 02:19 AM   #3
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Thanks for the tip, good service announcement.
Ozz is offline   Reply With Quote
Old 09-10-2013, 03:19 AM   #4
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Bob,
I found a slide-show on these outlets, I will post it if you don't mind, it reinforces your point.

https://picasaweb.google.com/Jimsue13/20111221OutletBedroom?authuser=0&feat=directlink
Ozz is offline   Reply With Quote
Old 09-10-2013, 04:30 AM   #5
Irlpguy
Montana Master
 
Join Date: Oct 2012
Location: Chilliwack
Posts: 1,520
M.O.C. #12935
Good advise from the OP. We should not have to check these things, but the more we have to do with a trailer of any kind the more we find we should be aware of. This type of thing would never pass an S&B electrical inspection.

Although the author of the slide show tells you not to use a 20 amp outlet, he did just that. He also replaced a GFCI outlet with a standard outlet.

This does not seem like a good example of what to do, there now is no GFCI protection on that outlet.

Just sayin...
Irlpguy is offline   Reply With Quote
Old 09-10-2013, 04:37 AM   #6
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Ouch!
I stated...twice.. I was changing the outlet with the proper one.. perhaps a course in reading would be good?
Also, if you ..re-read.. the outlet was downstream for the GFI, a controlled outlet.
Oh, the author's name is Ozz
Is this beat up on the Ozzman day?
Just sayin...
Ozz is offline   Reply With Quote
Old 09-10-2013, 04:46 AM   #7
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Quote:
quote:Originally posted by Ozz

Ouch!
I stated...twice.. I was changing the outlet with the proper one.. perhaps a re-read would be good?
Also, if you ..re-read.. the outlet was downstream for the GFI, a controlled outlet.
Oh, the author's name is Ozz
Is this beat up on the Ozzman day?
Just sayin...
Ozz is offline   Reply With Quote
Old 09-10-2013, 04:51 AM   #8
DQDick
Site Team
 
DQDick's Avatar
 
Join Date: Jun 2011
Location: Wilsey
Posts: 18,799
M.O.C. #11455
Don't overlook the advice about the fire extinguisher. We have 5 in our rig and an escape ladder. 4 of them are non-toxic so if necessary you can spray them on yourself to get thru the flames.
__________________
Dick, Joyce, Diego, Picatso and Gustav
2017 3720 RL, and 2013 HC 343RL
Pullrite Hitch, IS, Disk Brakes, 3rd AC, Winegard Traveler, Bathroom door mod, Dometic 320, couch for desk swap, replaced chairs, sun screens, added awnings, etc.
DQDick is offline   Reply With Quote
Old 09-10-2013, 05:19 AM   #9
Irlpguy
Montana Master
 
Join Date: Oct 2012
Location: Chilliwack
Posts: 1,520
M.O.C. #12935
No, not picking on you at all OZZ, my eyes are not that great anymore but the first picture appears to be a GFCI box, when the project was finished it looks to me like a GFCI box was replaced with a regular box.

I read and re-read the text twice before my post and again now, I cannot see where it says it is downstream from a GFI breaker, maybe what I am seeing is "not" what I think I am seeing.

I know you were not suggesting someone replace a GFI outlet with a non GFI outlet, to me the pictures indicated that was what was done. Electrical wiring can be confusing to anyone with no familiarity with it, I did not want anyone to be doing the wrong thing.
Irlpguy is offline   Reply With Quote
Old 09-10-2013, 05:34 AM   #10
Chip
Montana Fan
 
Join Date: Oct 2006
Location: Friendship, Maine
Posts: 483
M.O.C. #6338
After reading these posts I checked my spare outlet, and of course it is a 20 amp. I better add a 15 amp to my spare parts.

Thanks for the post and pictures Ozz. Appreciate it.

__________________

2012 Big Sky 3400, now an SOB 5th wheel
2007 Montana 3075 previously
2015 GMC 3500 Dually
Chip is offline   Reply With Quote
Old 09-10-2013, 06:04 AM   #11
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
The first picture states it is a controlled outlet from the GFI.
No problem, I have tough skin. It just surprised me about the 'coldness' of the response, I was just trying to help.
I probably should have not infringed on Bob's thread, probably bad manners. Sorry Bob. Again, just trying to help.
You are welcome, Chip. A lot of times we are in a place without a hardware store and make do.
Ozz is offline   Reply With Quote
Old 09-10-2013, 06:05 AM   #12
2BsRetired
Established Member
 
Join Date: Feb 2011
Location: Coquitlam
Posts: 12
M.O.C. #11106
Send a message via Yahoo to 2BsRetired
Great advice from all of you, however OZZ in the pictures that you posted at the website I noticed that there was NO box used to install the outlet. This is against all electrical codes anywhere. I used a shallow box to be able to fit in the walls then an extension box like is used for most of our GFCI outlets. This will make the outlet proud of the wall. Also in the wall at the top and bottom of the shallow box I put a piece of 3/8 plywood to have something to attach the box to other than just the paneling in the rig. (more support) This method gives you the space needed to do a proper job. By not using a box in the wall it becomes just or even more unsafe as the outlets used during the manufacturing.
2BsRetired is offline   Reply With Quote
Old 09-10-2013, 06:08 AM   #13
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
I used a rework box, I cut the back off of it, it is in the slideshow. The box has 'ears' that secure it to the wallboard.
That may be visible in the slideshow.
Ozz is offline   Reply With Quote
Old 09-10-2013, 06:17 AM   #14
2BsRetired
Established Member
 
Join Date: Feb 2011
Location: Coquitlam
Posts: 12
M.O.C. #11106
Send a message via Yahoo to 2BsRetired
Hi again OZZ sorry to burst your bubble however you cannot cut the back of the box off as this is against code as it leaves the outlet open to the inside of the wall.
2BsRetired is offline   Reply With Quote
Old 09-10-2013, 06:26 AM   #15
2BsRetired
Established Member
 
Join Date: Feb 2011
Location: Coquitlam
Posts: 12
M.O.C. #11106
Send a message via Yahoo to 2BsRetired
Great advice from all of you, however OZZ in the pictures that you posted at the website I noticed that there was NO box used to install the outlet. This is against all electrical codes anywhere. I used a shallow box to be able to fit in the walls then an extension box like is used for most of our GFCI outlets. This will make the outlet proud of the wall. Also in the wall at the top and bottom of the shallow box I put a piece of 3/8 plywood to have something to attach the box to other than just the paneling in the rig. (more support) This method gives you the space needed to do a proper job. By not using a box in the wall it becomes just or even more unsafe as the outlets used during the manufacturing. Sorry I made a second post and did not just reply to this one I am a newbe to this. Check the second post.
2BsRetired is offline   Reply With Quote
Old 09-10-2013, 06:49 AM   #16
Irlpguy
Montana Master
 
Join Date: Oct 2012
Location: Chilliwack
Posts: 1,520
M.O.C. #12935
Ozz my post was not intended to be cold, I also was trying to help. It is not good practice for those unfamiliar with electrical wiring to do their own work, and some would not tackle it on their own.
For you and others the job is doable and you are unlikely to wire something incorrectly, my concern was only that someone do something they should not do.

After rubbing my eyes and having another coffee I see the outlet is clearly not a GFCI outlet itself. I am glad that your picture taking skills have improved with the many other projects you have posted.

Your intent was to add to what the OP had said, that is what it is all about. No offense intended as originally I did not think it was your own project, but should have known that.


Irlpguy is offline   Reply With Quote
Old 09-10-2013, 07:19 AM   #17
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Quote:
quote:Originally posted by 2BsRetired

Hi again OZZ sorry to burst your bubble however you cannot cut the back of the box off as this is against code as it leaves the outlet open to the inside of the wall.
Bubble is in tact, the outside of the wall is flush with the back of the box, sometimes a guy has to do what he has to do
Ozz is offline   Reply With Quote
Old 09-10-2013, 07:19 AM   #18
bncinwv
Montana Master
 
Join Date: Feb 2007
Location: Winfield
Posts: 7,327
M.O.C. #6846
Time for me to get educated here. Unless I am completely out in left field here, I was not aware of an "electrical code" for RV's. Rv's are classified as vehicles (they have a VIN), and are not a fixed structure. Now granted, there are some common sense aspects of the NEC that "should" be applied, but I am unaware of any regulatory oversight of any nature. Comments?
Bingo
__________________

Bingo and Cathy - Our adventures begin in the hills of WV. We are blessed by our 2014 3850FL Big Sky (previous 2011 3750FL and 2007 3400RL) that we pull with a 2007 Chevy Silverado Classic DRW CC dually.
bncinwv is offline   Reply With Quote
Old 09-10-2013, 07:21 AM   #19
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Quote:
quote:Originally posted by Ozz

I used a rework box, I cut the back off of it, it is in the slideshow. The box has 'ears' that secure it to the wallboard.
That may be visible in the slideshow.
CRS, I remember it was a communication box.. I think. I have slept since I bought the box.
Ozz is offline   Reply With Quote
Old 09-10-2013, 07:29 AM   #20
Ozz
Montana Master
 
Join Date: Jul 2006
Location: K.C.
Posts: 11,731
M.O.C. #5980
Bingo, I am so deep in the doghouse I shouldn't comment, but I THINK I agree with you. maybe..
Ozz is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Non-working Electrical Outlets buckshot Montana Problems, Problem Solving & Technical Help 8 10-29-2016 02:14 PM
Electrical Outlets don't work jimso Montana Problems, Problem Solving & Technical Help 12 07-23-2009 05:48 AM
Outlets? You need more outlets, or lighting? Ozz Additions & Improvements 1 11-23-2007 01:04 PM
Electrical Outlets in the basement ken Additions & Improvements 3 07-18-2005 01:03 PM
Electrical Outlets??? palebluedot Montana Problems, Problem Solving & Technical Help 0 11-02-2003 02:21 AM