We may be camping in a spot we will require a longer electrical cord for 50 amp service. I wont use one if not necessary.


Any suggestions or concerns in this situation.
Should I buy a manufactured cord or build it myself? I have the wire but need yo buy the ends.
mbjam359 is offline   Reply With Quote
Old 06-11-2018, 11:33 AM   #2
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,172
M.O.C. #6433
There is no problem using a well made extension cord. I bought one since I wanted molded waterproof connectors on such end. Got lucky and found a good sale at the same time I anted one.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-11-2018, 03:16 PM   #3
jcurtis934
Montana Master
 
Join Date: Sep 2013
Location: Pensacola (mail forward service)
Posts: 3,198
M.O.C. #13740
I bought mine and have had no issues. Have had to use it several times when I run into a rv park that has its pedestals too far forward...as now at harpers ferry koa.
__________________
2012 F350 6.7 L dually, 2013 3800RE with 6 pt leveling, Sumitomo 17.5" load range h tires, Samsung 18 cu ft residential fridge, 8k Morryde I.S. with disc brakes. Full timing since 2012.
jcurtis934 is offline   Reply With Quote
Old 06-27-2018, 04:17 PM   #4
Jbbev
New Member
 
Join Date: May 2018
Location: Madison
Posts: 7
M.O.C. #21847
What’s a good price I should look for? Say a 30 foot extension.
Jbbev is offline   Reply With Quote
Old 06-27-2018, 06:17 PM   #5
DebNJim B
Montana Master
 
DebNJim B's Avatar
 
Join Date: Jan 2018
Location: Northville, NY
Posts: 807
M.O.C. #21158
I paid $60 for my 15 footer.
DebNJim B is offline   Reply With Quote
Old 06-11-2018, 04:13 PM   #6
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
We carry a 50 amp extension cord with us at all times. It is of good quality. We have used it on many occasions since 2006 with not a problem.
richfaa is offline   Reply With Quote
Old 06-11-2018, 04:15 PM   #7
DQDick
Site Team
 
DQDick's Avatar
 
Join Date: Jun 2011
Location: Wilsey
Posts: 18,799
M.O.C. #11455
We carry a high quality one that I got on sale cheaper than what the plugs would cost to make it myself.
DQDick is offline   Reply With Quote
Old 06-11-2018, 05:33 PM   #8
cpaulsen
Montana Fan
 
cpaulsen's Avatar
 
Join Date: Feb 2016
Location: Brookings
Posts: 313
M.O.C. #18275
Same here..bought a 25 footer.....cheaper then I could make one.
cpaulsen is offline   Reply With Quote
Old 06-12-2018, 07:09 PM   #9
MARK A
Montana Master
 
Join Date: Jan 2016
Location: STAYTON
Posts: 1,118
M.O.C. #18157
Quote:
Originally Posted by mbjam359 View Post
We may be camping in a spot we will require a longer electrical cord for 50 amp service. I wont use one if not necessary.


Any suggestions or concerns in this situation.
Should I buy a manufactured cord or build it myself? I have the wire but need yo buy the ends.
You can’t buy the stuff to make them for what they cost.

Mark
MARK A is offline   Reply With Quote
Old 06-23-2018, 07:07 AM   #10
Wyatt Earp
Established Member
 
Join Date: May 2018
Location: Newport
Posts: 45
M.O.C. #21746
What lengths do you have? I'm looking at 15' but a 30' isn't that much more. Do you need to worry about line loss with a longer cord?
__________________
2018 Montana 3121RL, 35 feet of home away from home.
2018 Chevy 3500HD, 4WD, Double Cab, SRW, 8' bed, Summit White with stump pulling diesel.
Wyatt Earp is offline   Reply With Quote
Old 06-23-2018, 07:48 AM   #11
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
We have two 15 foot extensions and have used them a couple of times at fair grounds . We did not see a loss.
richfaa is offline   Reply With Quote
Old 06-23-2018, 12:46 PM   #12
Texan
Montana Master
 
Join Date: May 2017
Location: new caney
Posts: 1,050
M.O.C. #19873
Same here. I have the 15' extension cord and needed it every time i plugged in at home until i moved my pedestal closer. I've used the 15' a few times traveling but never needed more than the 15'. I've seen no problem with the 15' but you would have a little drop if using an 50' extension cord. I don't think i would go over 25' for an extension cord.
Texan is offline   Reply With Quote
Old 06-23-2018, 01:16 PM   #13
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,172
M.O.C. #6433
Voltage drop is directly proportional to current and resistance, V=IR. Resistance for a 25’ 50 amp cord would be about 0.0004 ohms per foot of wire. About 0.02 ohms for length of the 25’ cable (25’ of wire for each direction = 50’). At full 50 amps the total voltage drop would be about 1 volt. At 25 amps the voltage drop would be about 0.5 volts. There would be another very small drop due to the additional plug connection. But that would be there whether the cord length was 15’, 25’, or 50’. Since you are not likely to be approaching full current you can see that voltage drop due to the extension cord is of little concern.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-23-2018, 02:35 PM   #14
richfaa
Montana Master
 
Join Date: Jan 2005
Location: North Ridgeville
Posts: 20,229
M.O.C. #2839
Quote:
Originally Posted by BB_TX View Post
Voltage drop is directly proportional to current and resistance, V=IR. Resistance for a 25’ 50 amp cord would be about 0.0004 ohms per foot of wire. About 0.02 ohms for length of the 25’ cable (25’ of wire for each direction = 50’). At full 50 amps the total voltage drop would be about 1 volt. At 25 amps the voltage drop would be about 0.5 volts. There would be another very small drop due to the additional plug connection. But that would be there whether the cord length was 15’, 25’, or 50’. Since you are not likely to be approaching full current you can see that voltage drop due to the extension cord is of little concern.

I was just going to say that.
richfaa is offline   Reply With Quote
Old 06-27-2018, 01:59 PM   #15
worleyjrtx5
Seasoned Camper
 
Join Date: Mar 2014
Location: Copperas Cove
Posts: 68
M.O.C. #14165
Smile 50 Amp Extensions

Look on Craigslists/Facebook Sales. Found mine on Craigslists, two 15 ft. Both nearly new. Guy was getting out of RV'ing. 1/3 d the price.
worleyjrtx5 is offline   Reply With Quote
Old 06-28-2018, 06:09 PM   #16
packnrat
Montana Fan
 
Join Date: May 2018
Location: san andreas
Posts: 209
M.O.C. #21805
Quote:
Originally Posted by BB_TX View Post
Voltage drop is directly proportional to current and resistance, V=IR. Resistance for a 25’ 50 amp cord would be about 0.0004 ohms per foot of wire. About 0.02 ohms for length of the 25’ cable (25’ of wire for each direction = 50’). At full 50 amps the total voltage drop would be about 1 volt. At 25 amps the voltage drop would be about 0.5 volts. There would be another very small drop due to the additional plug connection. But that would be there whether the cord length was 15’, 25’, or 50’. Since you are not likely to be approaching full current you can see that voltage drop due to the extension cord is of little concern.
i do not get it.
a extenson cord can have loss?
but hard wall wire does not?
or am i missing something here?
packnrat is offline   Reply With Quote
Old 06-28-2018, 06:28 PM   #17
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,172
M.O.C. #6433
Quote:
Originally Posted by packnrat View Post
i do not get it.
a extenson cord can have loss?
but hard wall wire does not?
or am i missing something here?
All wire, including the wire in your house, has some amount of inherent resistance. And that resistance does cause some voltage drop proportional to the current flowing thru it. Done correctly, wire is sized so that the resistance (and therefore the voltage drop) is minimal for the amount of current that particular wire is expected to carry. The larger the wire the less the resistance and the less voltage drop for a defined current over the length of that wire.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-30-2018, 01:32 PM   #18
Nighthawk
Seasoned Camper
 
Nighthawk's Avatar
 
Join Date: Apr 2010
Location: Surrey
Posts: 68
M.O.C. #10340
50 Amp Plug

Yes, the 50 amp cords are heavy. I have camped a few times where my cord does not reach the pedestal. Instead of an extension cord, I added another 50 amp receptacle close to the service centre where the feed from the factory receptacle at the rear of the trailer ends up (at the service panel). I used #8 wire, heavy enough for 50 amps and tied into the existing cable going to the service panel. I only needed a few feet of wire. To avoid the rear being hot when plugged into the side receptacle, you might want to use a transfer switch.

Now I can plug into the back or the trailer or the side of the trailer with no need for an extension cord. I use my installed side receptacle most of the time as the pedestals are usually near the centre of the campsite. It has been very convenient.

I don't know why Keystone, and other mfg, put the power receptacle at the rear of the trailer, then run a long heavy cable in the trailer belly to the front/centre of the trailer where the service panel often is located. I'm convinced the designers of trailers have never gone RV-ing!
Nighthawk is offline   Reply With Quote
Old 06-30-2018, 05:36 PM   #19
mbjam359
Seasoned Camper
 
Join Date: Aug 2017
Location: Dayton
Posts: 66
M.O.C. #20338
We just got home from the trip that I thought I might need on. I took a chance and did not purchase one and had little to spare. It was close but we had some options.
mbjam359 is offline   Reply With Quote
Old 07-01-2018, 04:13 PM   #20
masterdrago
Montana Master
 
masterdrago's Avatar
 
Join Date: Sep 2017
Location: Willis
Posts: 896
M.O.C. #20587
Quote:
Originally Posted by Nighthawk View Post
I don't know why Keystone, and other mfg, put the power receptacle at the rear of the trailer, then run a long heavy cable in the trailer belly to the front/centre of the trailer where the service panel often is located. I'm convinced the designers of trailers have never gone RV-ing!
The only 5r I've seen with the power plug at the rear was a 3 year old Cardinal by Forest River. My experience is rather limited (shopped for 10 months - owned for 8). Our 2018 Montana has the plug just aft of the axles port side (slightly south of middle).
__________________
2018 Montana 3791RD (SOLD)
2017 Ram 3500 DRW 6.7 Cummins Aisin, B&W RVK3600 (SOLD)
masterdrago is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:25 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.