ONAN 5500 Gold Marquis Rookie - Need Advice
Our 2013 Montana 3750FL has a built in LP generator and it is our first ONAN. Beyond the routine maintenance driven by the hours of use, what advice or recommendations, do's and don't, can you offer an ONAN rookie? Is an exhaust extension recommended and if so, which one? Do I need to exercise it once a month during the winter? Do I need to do anything to winterize it? Can you run it for long periods of time? Should it be shut off when we leave our site? Those a just come questions that come to mind. Any advice would be appreciated.
|
|
|
12-10-2012, 03:18 PM
|
#2
|
Montana Master
Join Date: Feb 2007
Location: Winfield
Posts: 7,327
M.O.C. #6846
|
All I can offer is my limited knowledge after having used ours for two years now. It should be "exercised" once a month during the winter with a load applied. The manual recommends about an hour a month. There is no winterization needed. It can run for extended periods of time provided it has fuel and oil, if it is propane, it will suck a little over a gallon an hour. A 30 pound tank has about 7 gallons and a 40 pound tank has about 9 gallons, so run-time is limited. I would not advise leaving it on when you leave the site. We do not have an exhaust extension but have experienced the need for one and are looking at the "Venturi" type exhaust system that clamps to the side of the rig to get the exhaust above the rig's roof for the wind to disperse it. One thing about winter is they can be subject to dying dependent on the outside temperature due to the vaporization process of the propane. Hope this helps and I am sure more seasoned users will chime in if I am off-base on anything.
Bingo
__________________
Bingo and Cathy - Our adventures begin in the hills of WV. We are blessed by our 2014 3850FL Big Sky (previous 2011 3750FL and 2007 3400RL) that we pull with a 2007 Chevy Silverado Classic DRW CC dually.
|
|
|
12-10-2012, 03:27 PM
|
#3
|
Montana Fan
Join Date: Jul 2010
Location: Ludlow
Posts: 124
M.O.C. #10557
|
Quote:
quote:Originally posted by bncinwv
All I can offer is my limited knowledge after having used ours for two years now. It should be "exercised" once a month during the winter with a load applied. The manual recommends about an hour a month. There is no winterization needed. It can run for extended periods of time provided it has fuel and oil, if it is propane, it will suck a little over a gallon an hour. A 30 pound tank has about 7 gallons and a 40 pound tank has about 9 gallons, so run-time is limited. I would not advise leaving it on when you leave the site. We do not have an exhaust extension but have experienced the need for one and are looking at the "Venturi" type exhaust system that clamps to the side of the rig to get the exhaust above the rig's roof for the wind to disperse it. One thing about winter is they can be subject to dying dependent on the outside temperature due to the vaporization process of the propane. Hope this helps and I am sure more seasoned users will chime in if I am off-base on anything.
Bingo
|
Thanks for your information. Im not sure about exercising the ONAN during the winter because it is covered, and they put the switch in a cabinet up front that I cant reach with side outs closed. Sounds like a bad situation! Where did they put the switch in your model year?
|
|
|
12-10-2012, 03:32 PM
|
#4
|
Montana Master
Join Date: Feb 2007
Location: Winfield
Posts: 7,327
M.O.C. #6846
|
There is also a start switch accessible from the outside. Simply open the front compartment and remove the front cover of the generator and there is a start switch at the upper left hand corner of the unit. You don't even have to go in the rig other than to turn things on to provide the load for the genny.
Bingo
|
|
|
12-10-2012, 05:03 PM
|
#5
|
Montana Fan
Join Date: Nov 2008
Location: Placerville
Posts: 357
M.O.C. #8962
|
We have had ours for 3.5 years, great generator. They use fuel, run it all day, it will use one of your propane bottles, I have the Gen-Turi exhaust extention, it sends the exhaust up not out, it is good if you have a rig next door, as in Quartzsite in the Circle, as for noise it helps a little, being an LPG run engine, the fumes are really nothing at all. I service ours once a year, oil 2 quarts, (Shell Rotella 15w40, new oil filter, and clean the air filter, very simple,
|
|
|
12-10-2012, 05:20 PM
|
#6
|
Montana Master
Join Date: Nov 2003
Location: Santa Fe Springs
Posts: 4,189
M.O.C. #639
|
Why would you need a exhaust extention? its on propane, and a lot safer than gas exhaust thats why they are on fork lifts inside factory buildings. The extention could cause more back pressure on the engin and cause a problem else where.
Run it monthly under load, the Air conditioner will give it that, or an electric heater. let its oil get to opperating temps before you go shutting it down.
__________________
Pulling a 2004, 2980 RL an oldie but goodie.
Tow vehicle is a 2009 RED RAM 3500 DRW.
|
|
|
12-10-2012, 11:35 PM
|
#7
|
Seasoned Camper
Join Date: Oct 2010
Location: boerne
Posts: 57
M.O.C. #10842
|
On the dying in cold weater I tried various pigtails at the tanks with no luck. Unit would sometimes die when furnace comes on. Guy at propane place said all the new pigtails have restrivtion in them. I switched to old hoses that screw to inside threads on bottle. Only drawback is have to use crescent wrench when removing hose for refill. I have not had gen shut down once since changing. Been in sub freezing weather many times.
|
|
|
12-10-2012, 11:37 PM
|
#8
|
Seasoned Camper
Join Date: Oct 2010
Location: boerne
Posts: 57
M.O.C. #10842
|
Quote:
quote:Originally posted by pappy65
On the dying in cold weater I tried various pigtails at the tanks with no luck. Unit would sometimes die when furnace comes on. Guy at propane place said all the new pigtails have restriction in them. I switched to old hoses that screw to inside threads on bottle. Only drawback is have to use crescent wrench when removing hose for refill. I have not had gen shut down once since changing. Been in sub freezing weather many times.
|
|
|
|
12-11-2012, 01:06 AM
|
#9
|
Montana Master
Join Date: Dec 2002
Location: Rapid City
Posts: 739
M.O.C. #77
|
I have been using my Onan for 4 years now. When I had it installed, I went with the gasoline option and had the controls mounted in front of the lavatory for easy access. I also had the on/off switch for my 3K inverter mounted in the same place. Gas is another fuel tank to contend with but is easier to refill than the propane (especially if you are as lazy as I am. )
We run the gen at least once a month. Oh, in your case you can run the gen from its own controls inside the front panel. If you do, be sure to replace the panel while it is running for proper cooling. That way you want have to run your slides out. Do make sure your exhaust is not restricted in any way by the cover.
As previously stated, annual maintenance is simple...change oil & filter...clean the air filter...done.
|
|
|
12-11-2012, 03:43 AM
|
#10
|
Montana Master
Join Date: Jun 2006
Location: Madison
Posts: 1,239
M.O.C. #5906
|
Don't know if there is a connection here, but during the storm Sandy we boondocked for a couple nights. I ran the generator so that the battery would stay up to power the furnace. During the night both the generator and furnace quit. The propane tank was still partially full but covered in frost. I asked some propane folks about what happened. They said that probably the combination of drawing propane for both the furnace and the generator at the same time caused the propane in the tank to be depleted too rapidly and that froze the remainder of the propane in the tank. Since then we have not run both at the same time and have not had a repeat of the frozen propane.
|
|
|
12-11-2012, 05:17 AM
|
#11
|
Montana Fan
Join Date: Feb 2007
Location: Bayswater
Posts: 317
M.O.C. #6781
|
Quote:
quote:Originally posted by DonandBonnie
Don't know if there is a connection here, but during the storm Sandy we boondocked for a couple nights. I ran the generator so that the battery would stay up to power the furnace. During the night both the generator and furnace quit. The propane tank was still partially full but covered in frost. I asked some propane folks about what happened. They said that probably the combination of drawing propane for both the furnace and the generator at the same time caused the propane in the tank to be depleted too rapidly and that froze the remainder of the propane in the tank. Since then we have not run both at the same time and have not had a repeat of the frozen propane.
|
The three factors you encountered are the rate of flow, outside temp and the level of propane in your tank. With a full tank you probably would not have had a problem and could run both the furnace and genny. The lower the tank goes, the lower the outside temp falls and you will soon intersect with the point where you will not get enough fuel to the generator. If you had another full propane tank then switch to that.
|
|
|
12-11-2012, 05:30 AM
|
#12
|
Montana Master
Join Date: Jun 2006
Location: Madison
Posts: 1,239
M.O.C. #5906
|
Jim,
I did try the changeover but the frozen propane was up into the regulator. The propane wouldn't flow until the outside temperatures went up enough for it to thaw out. Everything you have said is true. The good news is that the whole issue was a temporary inconvenience and just one more thing to add to our learning curve. Thankfully we weren't in deep freeze temperatures. At the time, we dipped to the high 20's overnight and rose to above freezing within a few minutes after sunrise.
|
|
|
12-11-2012, 05:58 AM
|
#13
|
Montana Master
Join Date: Apr 2009
Location: Murrieta
Posts: 5,816
M.O.C. #9257
|
Here is a link for why propane has problems in cold temps: http://www.ehow.com/facts_7597557_ca...ks-freeze.html
I'm guessing that when propane is being used quickly like with a furnace AND generator, one must keep the tanks more full to minimize the condensation phenomenon that can reduce the pressure in a propane bottle.
On Edit: This link explains that you might not want to let the propane bottles get too low, either: http://www.ehow.com/about_6659739_co...ne-tanks_.html
|
|
|
12-11-2012, 06:51 AM
|
#14
|
Montana Fan
Join Date: Jul 2010
Location: Ludlow
Posts: 124
M.O.C. #10557
|
Some great responses. So if my cover doesn't block the exhaust it seems safe to run the generator during the winter for 30 Minutes, once a month? To put it under load, I will have to run something electical, like a shop vac, off of the outside outlet on the camper. Everyday is one more day to camping season!
|
|
|
12-11-2012, 08:22 AM
|
#15
|
Montana Master
Join Date: Feb 2007
Location: Winfield
Posts: 7,327
M.O.C. #6846
|
Cover will not block the exhaust, it is out the bottom and carried to the off-side of the rig (at least on our factory installation). If I remember correctly, the manual recommends at least a half load, I don't think the shop vac will get you there, but I would think you would be okay, better yet, hook up a coffee pot outside so you can have warm refreshments, it will have a greater amperage draw!
Bingo
|
|
|
12-11-2012, 02:06 PM
|
#16
|
Montana Master
Join Date: Oct 2011
Location: Lykens
Posts: 545
M.O.C. #11842
|
If you find yourself in the position of having to use a lot of propane when it's cold you have to wrap the cylinders with a warming blanket.
http://m.globalindustrial.com/m/p/hv...arming-blanket
Also the exhaust extensions such as the genturi type do not create any back pressure.
I know from years of tailgating in the overnight RV lots at Penn State Football Games.
Some of the November games were pretty cold and snowy.
|
|
|
12-14-2012, 06:55 AM
|
#17
|
Seasoned Camper
Join Date: Nov 2008
Location: Sheffield
Posts: 74
M.O.C. #8921
|
The problem is that the propane is being drawn out to fast. In cold weather the tank won't even empty. A guy from the gas company told me that RV propane systems aren't designed to draw a lot of propane and what is really needed is to have both tanks draw at the same time to eliminate the problem. I have an onan 5500 and have had it freeze up in cold weather. As someone mentioned it is best to switch between tanks. As far as exhaust extension is concerned I have a Gen Turi extension and love it. Even though Propane fumes are not as toxic they still have CO which is deadly just less of it. A Gen Turi is great for close neighbors as it directs all gases up.
|
|
|
12-15-2012, 01:10 AM
|
#18
|
Montana Master
Join Date: Jan 2009
Location: Vermontville
Posts: 1,129
M.O.C. #9045
|
To put a load on your generator I always use a hair dryer and a heat gun. Both of them draw a great deal on the gen. This is on my 2000 Honda's. I believe thats quite a load and it sounds like it once I turn them on.
Dave
|
|
|
12-15-2012, 07:24 AM
|
#19
|
Montana Fan
Join Date: Jul 2010
Location: Ludlow
Posts: 124
M.O.C. #10557
|
I excersied the ONAN today for 30 minutes and plugged in a portable electrical heater. As advised here, strated it at the unti and reinstalled the cover while running, and let it go. No problms with the cover being on. I thought afterwards that the battery switch is off so it wasn't charging but that is a bit more of a project to reach with the cover on. I'll try it next time.
Rich
|
|
|
|