![Reply](/forums/images/mo/buttons/reply.gif) |
08-27-2023, 09:21 AM
|
#1
|
Montana Master
Join Date: Jan 2022
Location: Shingle Springs
Posts: 2,362
M.O.C. #30417
|
30 AMP to 50 AMP Adaptor
We camp at Coloma Resort on the American river often. Not all the river front sites have 50 amps. Half of them have two 30 amp outlets on their own breakers. Has anyone used on of these?
__________________
Tony & Donna & the best dog ever, Murphy.
2022 Montana HC, 295RL, Solar Flex 400, Onan 3600 LPG, 2K inverter, 200AH Lithium. 2020 GMC Denali 2500 6.6 Duramax, Demco 21K Auto Slide
|
|
|
08-27-2023, 09:59 AM
|
#2
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,224
M.O.C. #6433
|
I haven't, but being both are 30 amp connectors there should be no problem. It is the ones with one 15/20 amp being the problem as the 15/20 is typically a GFCI outlet that will trip.
But one caveat. If both 30 amp outlets are on the same hot phase, it is possible that if both 30 legs are used near their maximum current that you could exceed the 50 amp rating of the neutral wire. You would probably not normally be pulling a total of over 50 amps combined from the two, but it is possible. If the two 30 amp outlets are on different phases, then there is no concern as the neutral could never exceed 30 amps.
The two hot legs on the same phase are additive on the neutral wire. Meaning the neutral carries the total current of both hot legs. On standard 50 amp split phase, the neutral current is reduced by the difference between the two hot legs and never exceeds the 50 amp rating of each leg.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
08-28-2023, 05:18 AM
|
#3
|
Montana Master
Join Date: Oct 2019
Location: Jacksonville
Posts: 2,182
M.O.C. #25165
|
I use one quite often at SC parks we frequent. All of their sites tend to have 2-30amp breakers but no 50amp. I haven't noticed any issues running everything off AC. I even run the water heater off AC and not propane without any problems.
I also do not have washer and dryer yet, so that may make a difference. The air conditioners are typically our largest draw and both of them will run on 30amp with little else running.
__________________
Robert & Diana McNeal
2019 Montana Legacy 3791RD 20th Anniversary Edition
2014 F350 4x4 6.7L SRW
|
|
|
08-28-2023, 06:22 AM
|
#4
|
Montana Master
Join Date: May 2019
Location: Alton
Posts: 2,768
M.O.C. #24086
|
I would wonder how they have two 30A receptacles wired.
Are they BOTH on the same circuit?
Are they wired separately one on L1 hot and the other on L2 hot?
Pay attention to what BB-Tx said in his 2nd paragraph. Having L1 and L2 on a 50A receptacle the opposite phase cancels out on the neutral wire so it doesn't carry too much current.
Picture is how 50A pedistal is wired.
|
|
|
08-28-2023, 08:18 AM
|
#5
|
Montana Master
Join Date: Jan 2022
Location: Shingle Springs
Posts: 2,362
M.O.C. #30417
|
One has to assume that if they have two 30 amp and one 20 amp outlets each with their own breakers that it would be wired to handle 80 amps?
__________________
Tony & Donna & the best dog ever, Murphy.
2022 Montana HC, 295RL, Solar Flex 400, Onan 3600 LPG, 2K inverter, 200AH Lithium. 2020 GMC Denali 2500 6.6 Duramax, Demco 21K Auto Slide
|
|
|
08-28-2023, 10:14 AM
|
#6
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,224
M.O.C. #6433
|
Quote:
Originally Posted by Foldbak
One has to assume that if they have two 30 amp and one 20 amp outlets each with their own breakers that it would be wired to handle 80 amps?
|
Yeah, I agree they should. But even if they are wired to handle 80 amps, the potential issue is with your trailer wiring and power cord. That wire is sized for 50 amps. And even though there are two hot legs of 50 amps each there is only one neutral wire. But due to the nature of how split phase 50 amps works, the neutral wire will never carry more than 50 amps. And normally much less. Split phase means the two hots always have neutral current flowing in opposite directions. So self canceling on the single neutral wire. If, for example, hot 1 was carrying 40 amps and hot 2 was carrying 30 amps, the neutral wire would only be carrying 10 amps. The 10 amps being the difference between the two. Pretty easy to see how that works with an electrical schematic but a little harder to clearly put it into words.
If the two 30 amp outlets were on the same phase, then both hots would always have neutral current flowing in the same direction and the neutral current would be the total of the two. For example, if both hots were carrying 25 amps the neutral would be carrying 50 amps. So with 30 amp outlets it would be possible to exceed the 50 amp wire sizing.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
08-28-2023, 02:25 PM
|
#7
|
Montana Master
Join Date: Jan 2022
Location: Shingle Springs
Posts: 2,362
M.O.C. #30417
|
Quote:
Originally Posted by BB_TX
Yeah, I agree they should. But even if they are wired to handle 80 amps, the potential issue is with your trailer wiring and power cord. That wire is sized for 50 amps. And even though there are two hot legs of 50 amps each there is only one neutral wire. But due to the nature of how split phase 50 amps works, the neutral wire will never carry more than 50 amps. And normally much less. Split phase means the two hots always have neutral current flowing in opposite directions. So self canceling on the single neutral wire. If, for example, hot 1 was carrying 40 amps and hot 2 was carrying 30 amps, the neutral wire would only be carrying 10 amps. The 10 amps being the difference between the two. Pretty easy to see how that works with an electrical schematic but a little harder to clearly put it into words.
If the two 30 amp outlets were on the same phase, then both hots would always have neutral current flowing in the same direction and the neutral current would be the total of the two. For example, if both hots were carrying 25 amps the neutral would be carrying 50 amps. So with 30 amp outlets it would be possible to exceed the 50 amp wire sizing.
|
Thanks Bill. I think I understand what you're saying. So as long as I don't pish it I should be ok? Meaning if I'm running both AC's and a TV. Don't turn on the microwave?
__________________
Tony & Donna & the best dog ever, Murphy.
2022 Montana HC, 295RL, Solar Flex 400, Onan 3600 LPG, 2K inverter, 200AH Lithium. 2020 GMC Denali 2500 6.6 Duramax, Demco 21K Auto Slide
|
|
|
08-31-2023, 08:43 AM
|
#8
|
Montana Master
Join Date: Oct 2014
Location: Hagerstown
Posts: 876
M.O.C. #16013
|
no 3rd a/c heat pump
Quote:
Originally Posted by Foldbak
Thanks Bill. I think I understand what you're saying. So as long as I don't pish it I should be ok? Meaning if I'm running both AC's and a TV. Don't turn on the microwave?
|
Way to much thought in monitoring the use of power and potential for mistakes before your first cup of coffee, "wait can I turn on the coffee maker"? "Is that the wife using her hair drier"? Let me check and see if both a/c`s are on. Just go to Home Depot and buy an inexpensive voltage tester capable of testing for 220 volts. Then when you get to the campground test the 2 30 amp plugs for split phase circuitry it will tell you what you have to work with. $19 on Ebay, Home Depot
__________________
2018.5 3791 Rear Den Montana, on the lake ![Fishing](images/rvsmilies/fishing.gif) no 3rd A/C, Mini Split, just do it
Electric Brakes ![EEK!](images/smilies/eek.gif) ..... Disk Brakes, it`s the only way
F350 Ford Dually 4:10`s w/bags (payload 5595 lbs) Sumo Springs 63 gal aux tank
Reese Goosebox Mor/Ryde SRE 4000 X Factors Monroe shocks.... real smooth ride
|
|
|
09-04-2023, 11:33 AM
|
#9
|
Site Team
Join Date: Apr 2017
Location: Colorado Rockies
Posts: 1,949
M.O.C. #19755
|
Quote:
Originally Posted by BB_TX
Yeah, I agree they should. But even if they are wired to handle 80 amps, the potential issue is with your trailer wiring and power cord. That wire is sized for 50 amps. And even though there are two hot legs of 50 amps each there is only one neutral wire. But due to the nature of how split phase 50 amps works, the neutral wire will never carry more than 50 amps. And normally much less. Split phase means the two hots always have neutral current flowing in opposite directions. So self canceling on the single neutral wire. If, for example, hot 1 was carrying 40 amps and hot 2 was carrying 30 amps, the neutral wire would only be carrying 10 amps. The 10 amps being the difference between the two. Pretty easy to see how that works with an electrical schematic but a little harder to clearly put it into words.
If the two 30 amp outlets were on the same phase, then both hots would always have neutral current flowing in the same direction and the neutral current would be the total of the two. For example, if both hots were carrying 25 amps the neutral would be carrying 50 amps. So with 30 amp outlets it would be possible to exceed the 50 amp wire sizing.
|
It's nice to have experts to think about this stuff. Showing an oscilloscope on the two legs, in-phase then out-of-phase, might make it clear.
__________________
Scott & Alta
2017 Montana 3160RL, Legacy, Onan 5.5Kw, Solar
2022 F-450 Lariat Ultimate
|
|
|
09-04-2023, 12:38 PM
|
#10
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,224
M.O.C. #6433
|
Quote:
Originally Posted by scottz
It's nice to have experts to think about this stuff. Showing an oscilloscope on the two legs, in-phase then out-of-phase, might make it clear.
|
Yeah, a schematic diagram along with a phase diagram helps visualize how/why current of the two separate hot legs flows in the common neutral wire in the same direction (same phase & additive) or in opposite directions (opposite phases & canceling).
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
08-28-2023, 03:36 PM
|
#11
|
Montana Master
Join Date: Dec 2009
Location: Sebring
Posts: 3,665
M.O.C. #9969
|
Using that type of adapter you're limited to only 30 amps per leg vs a true 50 outlet that gives you 50 amps per leg.
So if Keystone screwed up (Heaven forbid) and put both ACs on the same leg you would stand a good chance of tripping one of those 30 amp breakers if running both ACs.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
|
|
|
08-28-2023, 04:17 PM
|
#12
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,224
M.O.C. #6433
|
If your circuit breakers are clearly marked as to what they power you can make a reasonable estimate of what each leg will be carrying with those items on. Then you can determine what you can run and stay below 25 amps on each leg.
Some day I am going to sit down and draw some schematics of the 120/240 VAC power system and turn them into pictures I can post to help explain what I am trying to put in words.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
08-30-2023, 07:58 PM
|
#13
|
Montana Master
Join Date: Jan 2022
Location: Shingle Springs
Posts: 2,362
M.O.C. #30417
|
Quote:
Originally Posted by BB_TX
If your circuit breakers are clearly marked as to what they power you can make a reasonable estimate of what each leg will be carrying with those items on. Then you can determine what you can run and stay below 25 amps on each leg.
Some day I am going to sit down and draw some schematics of the 120/240 VAC power system and turn them into pictures I can post to help explain what I am trying to put in words.
|
Thanks Bill. I got a clear picture in a foggy head
__________________
Tony & Donna & the best dog ever, Murphy.
2022 Montana HC, 295RL, Solar Flex 400, Onan 3600 LPG, 2K inverter, 200AH Lithium. 2020 GMC Denali 2500 6.6 Duramax, Demco 21K Auto Slide
|
|
|
08-31-2023, 03:41 AM
|
#14
|
Montana Master
Join Date: Dec 2021
Location: Northeast TX
Posts: 971
M.O.C. #30262
|
Only one sip of coffee before reading this thread and pretty sure y'all broke my head this morning! I followed it okay, but should have saved this one to read later on in the day
__________________
![](image.php?u=30262&type=sigpic&dateline=1662708055) Lee, Edith, Lil' Bit & Cuddles
22 MHC 331RL, Surge Guard 35550, SumoSprings, Kodiak disc brakes, 412Ah Lithium, Gen 3 Goosebox, Sailun 85s
22 Ram 3500 CC DRW 6.7 CTD Herrin Hauler Classic Bed, 45 gal AUX tank
|
|
|
08-31-2023, 06:51 AM
|
#15
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,224
M.O.C. #6433
|
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
08-31-2023, 07:30 AM
|
#16
|
Montana Master
Join Date: Aug 2004
Location: Livermore
Posts: 5,160
M.O.C. #1920
|
I felt a disturbance in the Force.
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
|
|
|
09-03-2023, 01:28 PM
|
#17
|
Montana Fan
Join Date: Apr 2018
Location: Peachtree City
Posts: 112
M.O.C. #21599
|
Yes. Works like a charm. Even carry a 30' 30 amp extension cord to reach the neighboring site (if not occupied).
__________________
2019 3931FB, 2011 F450 DRW KR
|
|
|
09-03-2023, 02:06 PM
|
#18
|
New Member
Join Date: Aug 2023
Location: Sheboygan
Posts: 9
M.O.C. #33230
|
We run a Hughs Watchdog in our power lines that would tell you what is going on with that setup. if there is a problem, it will tell you.
|
|
|
09-03-2023, 02:17 PM
|
#19
|
Montana Fan
Join Date: Apr 2018
Location: Peachtree City
Posts: 112
M.O.C. #21599
|
Yup...have that too
__________________
2019 3931FB, 2011 F450 DRW KR
|
|
|
09-04-2023, 11:18 AM
|
#20
|
Montana Fan
Join Date: Jun 2018
Location: Jacksonville
Posts: 383
M.O.C. #21993
|
I use that adapter from time to time, I have one that has a 20A and 30A, used it a few times also. One of the times I used the 30/30Y I plunged in one 30A and made a list of everything that worked then swapped them out and made a second list, nice to know what's on each leg.
__________________
I was once intelligent beyond my years. Now, I’m years beyond my intelligence.
2020 Montana 3561 Legacy, everything except paint.