Quote:
Originally Posted by PNW Fireguy View Post
I don't know of a way to feed both 50A legs of the PD from a single phase 120 invertor with a 60A transfer switch.
A 50A transfer switch has two separate poles and contacters (4 wire hookup - 2 hots, neutral and ground). The single pole output of the inverter gets jumpered to both hot legs of the inverter input. The output from the primary generator/shorepower ATS (part of the gen prep package) feeds into the other input of the secondary switch as two separate 50A legs.


So yes, loads are limited by the inverter at 3k when it's operating, but on gen or shore power, you are only limited by there respective capacities.


I had to install the second ATS to keep the hots and neutral isolated from the various power sources.