Sounds like the 30 amp cord is ok. Neutral and ground are normally bonded at the main distribution panel, so you should measure no voltage between those pins. You should measure a nominal 120 vac from the hot pin to the neutral pin. And a nominal 120 vac from the hot pin to the ground pin. Seems that is what you have.

So I would carefully check all wire connections in the 50 amp cord, particularly at the connector that is loose. And in your 50/30 adapter.