Electrical Power Inlet: Look Out!

The wife and I have been on the road in Sisters, Oregon for the last 10 days. A few days ago - all of a sudden - the TV, Microwave Oven, and Fireplace stopped working. This was the second time this had happened. The first time everything came back ON after about 20 minutes. This time the appliances didn't come back ON.....

So, I thought maybe a breaker had tripped. Checked the 5ers panel: all breakers ON... but I opened and re-closed all of them anyhow - you never know... no change: appliances still OFF. Went to the power pedestal (operating on the 50 Amp Service) and checked the breaker: it was ON but I opened and re-closed it anyhow. Still no change: appliances still off.

Went back to the 5ers panel and stared at it for a while... noted that all of the appliances that were OFF were fed by breakers on the right side of the panel. Got out the Volt Meter and started troubleshooting. First checked the Power Pedestal: 120 volts on each leg. Then went to the 5ers panel: found 120 volts on one leg and 0 volts on the other leg.

So, if there's power at the pedestal and no power at the 5ers breaker panel, the problem has to be somewhere between the two... Figured the most likely spot would be the Shore Power Inlet. First checked power at the end of the power cord: 120 volts on each leg: all good. Then noticed evidence of burning at one of the power prongs inside the Inlet Socket (see picture)... not good.

At that point I knew I had to take the Shore Power Inlet Socket out and see what was going on. Found a set screw on one of the power leg wires wasn't tight. The prong that was connected to that wire had brownish discoloration indicating arcing in the area. Next step was to take the whole assembly apart: sure enough, found the plastic around the prong had started to melt. Finally determined the root cause: one of the power leg wires had been inserted too far: the plastic insulation was partially in the clamp.

Over time, the insulation had gotten warm, deformed, and the clamp-to-wire connection loosened up. Arcing then developed and the connection failed completely. Thank goodness it didn't lead to a fire. When the Power Inlet was first installed at the factory, the technician probably tightened the terminal clamp just like the others: nice and snug.

Bought a new Shore Power Inlet online from Walmart (1.5 day delivery) and replaced the Inlet assembly. The installation instructions have a warning message in BOLD type: "Make certain there is no wire insulation under any terminal".

These connectors are very tricky to get right: you can't easily see the bare stripped wires and the end of the insulation when the wires are inserted into the terminals.

Hope this posting helps others that may experience intermittent electrical power problems that just don't seem to make sense. If you see any brownish discoloration at the Shore Power Inlet Prongs, check the wire terminations! Don't just tighten the terminal clamps: the wire insulation may be under the clamp - and like mine, the plastic that holds the prongs may have melted and deformed.
Attached Thumbnails
Click image for larger version

Name:	190709 Steve Miller RV Power Socket 2.jpg
Views:	86
Size:	132.7 KB
ID:	4140   Click image for larger version

Name:	190711 Power Inlet Terminal 1.jpg
Views:	73
Size:	145.8 KB
ID:	4141   Click image for larger version

Name:	190711 Power Inlet Terminal 2.jpg
Views:	69
Size:	176.3 KB
ID:	4142   Click image for larger version

Name:	190709 Steve Miller RV Power Socket 3.jpg
Views:	83
Size:	137.6 KB
ID:	4143  
__________________
Steve & Terri
2017 305RL Montana High Country
2017 F-250 CCSB Diesel Lariat FX4
SteveandTerri is offline   Reply With Quote