Was the park in question permitted, constructed and inspected per the National Electric Code (NEC)? 2014 NEC Article 551.73 states that when an electrical service for an RV has more than one receptacle, the load need only be calculated for the highest rated receptacle, which would be the 50 amp. The calculated load for a 50 amp receptacle shall be not less than 9600 volt-amperes, although a higher design load may have been used. There are load reduction factors used for multiple sites.

You can find a link to the 2014 NEC at the Oregon BCD website.